Hi, please can you see if this is correct for what I am trying to do.

I want 1 ring main circuit for sockets and another for lighting.

This is for a test lab that I am setting up at home.

The CU didn't come with any instruction so I want to make sure that I am doing it right and using the correct cabling.

Here is a picture :

consumer wiring.jpg

Thanks
 
Hi, please can you see if this is correct for what I am trying to do.

I want 1 ring main circuit for sockets and another for lighting.

This is for a test lab that I am setting up at home.

The CU didn't come with any instruction so I want to make sure that I am doing it right and using the correct cabling.

Here is a picture :

View attachment 39393

Thanks
Why would you want a lighting ring? a radial circuit would be the best option for a lighting circuit, and I suggest 1.5mm2 for the lights, not 2.5mm2, just saying.
 
Why would you want a lighting ring? a radial circuit would be the best option for a lighting circuit, and I suggest 1.5mm2 for the lights, not 2.5mm2, just saying.
Got a suspicion the OP is the same chap that said the college he attended used a PSU.
 
Why would you want a lighting ring? a radial circuit would be the best option for a lighting circuit, and I suggest 1.5mm2 for the lights, not 2.5mm2, just saying.

Sorry it was just the way I worded it.

I want 1 main ring for the sockets and another being a radial for the lighting.

Some people say 1mm is adequate for lighting but I don't mind using 1.5mm if I have to.

The feed to the CU is coming from a 13a plug as per the discussion we have the other week about setting up my lab.

Thanks
 
Why put a ring anyway - designed decades ago, old hat. I would consider radial sockets in 2.5 but you must replace the 32A MCB with 20A; design depends on the required socket load. As Pete999 states 1.5 for the lights, also in radial.
 
Sorry it was just the way I worded it.

I want 1 main ring for and another being a radial for the lighting.

Some people say 1mm is adequate for lighting but I don't mind using 1.5mm if I have to.

The feed to the CU is coming from a 13a plug.

Thanks
Use a flex, rather than twin and earth cable for the supply cable, 13 amp plug tops are not designed to accept twin and earth cable.
 
The feed to the CU is coming from a 13a plug.

So, what you have planned is totally pointless.
The circuit protection is on the 13A plug, so the 32A MCB in the garage will never ever in a million years trip because the maximum current will only ever be no more than 13amp.

So there is no point having a ring final, again because the current is limited to 13A.
Also I expect that the socket that the plug is in (at the house end?) is already RCD-protected? So there's no point in the RCD in the garage either.

So you could have saved your money on that garage unit, just run in the cable to a string of sockets and used a £3 FCU to provide the light switch and feed.
 
So, what you have planned is totally pointless.
The circuit protection is on the 13A plug, so the 32A MCB in the garage will never ever in a million years trip because the maximum current will only ever be no more than 13amp.

So there is no point having a ring final, again because the current is limited to 13A.
Also I expect that the socket that the plug is in (at the house end?) is already RCD-protected? So there's no point in the RCD in the garage either.

So you could have saved your money on that garage unit, just run in the cable to a string of sockets and used a £3 FCU to provide the light switch and feed.
I think the OP intends to build a testing board, to practice his ability for carrying out tests, it's not an ideal scenario, but I guess he will have account for the discrepancies, at least I think that's what he intends to do, but then again in this mad world of DIY electrics, who knows?
 
I think the OP intends to build a testing board, to practice his ability for carrying out tests, it's not an ideal scenario, but I guess he will have account for the discrepancies, at least I think that's what he intends to do, but then again in this mad world of DIY electrics, who knows?

As mentioned in a previous post. It's only for setting up a test lab for a couple of sockets and lights on a board!!

I'm fairly sure I stated that this is for a test lab. Sorry if some of you misunderstood my intentions.

I just want to make sure that I am using the right cabling.
 
As a test arrangement you have the wires going to the correct positions.
On the negative side live testing at this unit will involve your incoming supply unless it comes from a separated source.
As has been said your total load will be limited to the plug fuse rating and flex (up to 1.5mm²) should be used for the connection into the plug. Ideally the ends of the flex in the consumer unit should have ferrules on to ensure a safe connection into the screwed terminals without damaging the fine stranded cable.
As a design a 2.5mm² cable can only take 27A in the best circumstances and so cannot be protected by a 32A MCB, 25A at a pinch, 20A generally.
A consumer unit should not ideally have two different manufacturers protective devices as they may not line up correctly and so cause weak spots and high resistances at the busbar.
It starts off so easily doesn't it!
 
As a test arrangement you have the wires going to the correct positions.
On the negative side live testing at this unit will involve your incoming supply unless it comes from a separated source.
As has been said your total load will be limited to the plug fuse rating and flex (up to 1.5mm²) should be used for the connection into the plug. Ideally the ends of the flex in the consumer unit should have ferrules on to ensure a safe connection into the screwed terminals without damaging the fine stranded cable.
As a design a 2.5mm² cable can only take 27A in the best circumstances and so cannot be protected by a 32A MCB, 25A at a pinch, 20A generally.
A consumer unit should not ideally have two different manufacturers protective devices as they may not line up correctly and so cause weak spots and high resistances at the busbar.
It starts off so easily doesn't it!
Well spotted never noticed that, you are however right of course.
 

Reply to Help wiring Garage Consumer Unit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
455
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
775
Hey everyone, working on a new build house and outside garage is wired up like this, however customer wants a Garage Consumer Unit instead of the...
Replies
8
Views
311
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
747
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
686

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock