Discuss HeLp with 3 phase in the Australia area at ElectriciansForums.net

P

p11jor

Hi guys just need some help with 3 phase.I have done some theory on it a while back but not alot.So I get the fact there are 3 phase's and a neutral The three phases are colour coded and go to three separate parts on the 3phase db,Is this correct?What next? For the final circuits?Cheers for any help!
 
The 3 phases are brown, black and grey and will go into a 3 pole isolator on the 3 phase board. Then if you have 3 phase circuits coming from the board you fit the correct size tripple pole mcb. Then take the 3 phases to your socket/ isolator/ motor ect. You can also take single phase supplys from the board.
 
The thing to remember is to balance the load across all 3 phases. The total neutral current will be 0 amps if all phases are correctly balanced, ie like a induction motor. In reality you will rarely see a 100% balanced DB.All phases and neutral must be run through the same hole in any metallic containment or equipment, to stop eddy currents. With 3ph motors, if you want change the direction, you swap any 2 phases over.When testing, your PSCC should be measured between live and neutral and then multiplied by 1.732. Some say multiply by 2, but in some situations, this could cause quite a difference.I can't think of anything else at the mo, but I'm sure others wil help.
 
Also dont forget 3 phase is 415volts between phases and is very dangerous,take great care when working with it.
 
Last edited by a moderator:
If you have singe phase supplies fed from the board don’t go mounting sockets for example on different phases in close proximity to each other. There’s something about in the regs.
 
If you have singe phase supplies fed from the board don’t go mounting sockets for example on different phases in close proximity to each other. There’s something about in the regs.

Your meant to put a
<<<<< 400V Between >>>>>
Sticker on them..........

BUT... in a recent conversation with IQ he claims in the BGB they've removed the need for the 400v stickers
 
Flippin double post!!

Aahh I’m not the only one it’s happening to.

I still wouldn’t be happy with sockets in say an office with 415V between them.
OK we don’t know the situation this is going to be installed in, but it’s something to bear in mind.
 

Reply to HeLp with 3 phase in the Australia area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
657
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
777
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
672
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
852

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock