Hi, i need to know whether my calculation is correct.

I have 4 x 2.2kW Motors (3-phase) , i have a miniture 32 Amp breaker (Type D) but according to my calculation i require a 40 Amp breaker.

This is how i calculated it: 8800/(400x1.732) = 12.7 Amps per phase ---> 12.7x3 = 38 Amps

Was my calculation correct? If yes, will i require 6mm cable for this?

Thanks in advance.
 
Im asuming that you have this on a three phase supply so what you do require is a tripple pole C Type , this also depends wether you can reach the maximum permitted for a C type MCB on the circuit you are using it on
 

Reply to Help with breaker amp calculation in the Australia area at ElectriciansForums.net

Similar Threads

Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K
HI, I have a small shop space with single phase run to a 100amp breaker main, and I bought a few items such as a welder, plasma cutter and a...
Replies
3
Views
1K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock