chris.rigby

Hi,

I'm revising for my level 2 203 exam which I'm due to sit on Wednesday. I'm struggling a bit trying to get my head round power factors and lagging and leading..

One of the practice questions I have is:

What is the power factor of a circuit with a 4 ohms resistor and a 10 mH inductor?

The answer is 0.8 lagging but I don't know how this was calculated.

I know that PF = R/Z so if I divide 4 by 10 this gives me 0.4 and obviously if I multiply that by 2 then I get the answer of 0.8..but don't understand it. I'm also confused as to when it's lagging and when it's leading.

I'd appreciate any help you more experienced guys out there can give me.

Thanks in advance!
Chris
 
Cheers for that. I will print it off and read through it and hopefully that will help me get to grips with it!

If there's still something I don't understand - no doubt I will pop up here again!


Thanks again..
 
That is a bit of a hard question for lvl 2.

Are you sure you are not looking at 302 not 203 ;-)

This is off memory, but if wrong someone will come and slap me down in a sec.

The impedance of an inductor is 2 x pi x frequency x inductance.

so

Xl = 2 x 3.14 x 50 x 0.01.

And always remember the units of Ohms.

so doing a bit of sums you get 3.14 Ohms.

Pf= R/Z

Pf= 4 / 3.14

Pf ~= 0.8

And remember the units (Pf doesn't have any as a ratio).


Still think I might have this horribly wrong (bad nights sleep last night) so if wrong please correct me!


regarding leading and lagging a simple mnemonic always helps me.

CIVIL

Capacitance Current (symbol I) Voltage Current L (inductance)

So you either read right to left or left to right depending on whether cap or ind.

eg.

Cap so left current then voltage
Inductance so right hand side Voltage leads current


Hope this helps!
 
but are the resistor and coil in series or parallel? and 4/3.17 ain't 0.8.
 
That was it

Ok you have resistance of 4Ohm

Reactance of 3.14 Ohm

But formula says impedance.

Impedance = ROOT (r^2+L^2)

Impedance = ROOT (4^2+3.14^2)

Impedance = 5Ohm

Pf = R / Z
Pf = 4 / 5

Pf = 0.8


Hows it this time? =-)
 
Still a bitch of a question for LVL 2.

I didn't do my lvl 2, but jumped straight in to lvl3.
When I started lvl 3 most people in the class were struggling with Ohms law, we did not even cover powerfactor until late lvl3.
 
At college we didn't really cover this, yet it came up in my exam...which I failed, so now have the resit on Wednesday. Thanks for all the help on here - it's been more helpful than college has been!
 

Reply to Help with C&G 2330-203 level 2 question - just can't figure it out! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Advice on a London fast course to get C+G 2365 Level 2 - I am on a site in London as an electrical improver but I do need to finish my level 2...
Replies
1
Views
2K
Hi Everyone, New to the forum but hoping I can find a little help with my restoration project... I am adding a secondary wiring "system" to my...
Replies
14
Views
954
Hi all. In a bit of a situation which is starting to cause a fair bit of stress and figured maybe asking some silly questions here may help to...
Replies
7
Views
1K
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Howdy folks, new member here. Homeowner, been doing my own electric for 40 years or so, from swapping out plugs to installing an entire circuit...
Replies
2
Views
934

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock