Hi all,
Finally got around to installing UFH (loose cable type)
40sq metres being laid in a kitchen using 4 kits (10sqm each)
main heating source, 2000w per cable, Underfloor thermal board used on timber floor,
I was just wondering what amp size contactor to use to connect x4 cable to > stat.
(note.. I've actually ordered a 35amp contactor already but could change for another if unsuitable)
Also could someone help with the wiring diagram for such a module.
TIA
Also (yet another) i'm planing on fitting the stat about 300mm away from the combi boiler, Whould this effect the stat "thermostat" if i disable "air" stat and only use the floor probe? (thinking of the heat generated effecting the stat and reporting a false reading)
(Kitchen fitter as main trade, Part P Qualified)
Regards Dave