Discuss Help with Farm/Light industry diversity in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
13
Hi There,

Moving into deeper waters & needing a little assistance with calculating maximum demand/diversity on a farm/light industrial site planning to upgrade to 3 phase, add a car repair workshop, 63A events socket & allow for future proofing.

Current single phase setup:
Diversity for lights, sockets & heaters (Not compressor or ramps) taken into account.

-2 barns rarely used, sockets & lights 33A
-1 very small domestic dwelling with ground source heat pump 53.3A
-Small carpentry workshop attached to small barn inc. water heater 23.5A
-Tinkerer garage with 40A welder socket 57A
-Auto electrician with kitchen including water heater 44.5A
-Car workshop 17A
=228A

Additions planned:

Additional unit for car garage is being built which will have
-2 x small offices + workshop lights & sockets 38A
-3 x car ramps 16A
-1 x compressor 32A
-2 x water heaters 13A
-heating for offices 37A

63A events socket which will be rarely used
=199A

Allowance for 2 extra light industrial units/car workshops for future proofing.
=100A

I'm having difficulty calculating the required kVA for the 3 phase supply - call it lack of experience. Simply adding up the demand gives me 527A which would be 175A per phase requiring 3 phase 120kVA supply without PFC taken into acc. which I think it excessive.

Any advice on calculating the ideal supply would be much appreciated.

Chris
 
100 -120A per phase should be more than adequate. balancing the phases is critical.
 
Hi,that is quite an upgrade,have you enquired as to what is available?

Some of your anticipated loads are actual,some OCPD or socket ratings. You need to estimate with actual loads in mind,not just add up a row of DB sticker figures :)

Your customer may need to have a firmer idea of the requirements re:future proofing,as this may add considerably,to the cost of achieving their current plans.
 
Morning PEG,

An 80kVA upgrade is available although at considerable cost & a 3 phase conversation is definitely required for the new car garage.

Actual loads - this is where I ran into difficulties because the system usage varies so much, the actual load is minimal but the potential load is huge which I've tried to take into account following the diversity guidance. I can see areas where I could reduce the figures but I'm aware with the current setup & a slight change of use (barn to workshop conversion) a few heaters added then the demand rapidly increases.

The events supply is an additional buffer but maybe required on occasion.

Re: Future proofing. My customer is definitely keen to have some headroom for additions to the supply & there is plenty of space/opportunity for this.

It's a difficult decision to make but I appreciate your thoughts.

Chris
 

Reply to Help with Farm/Light industry diversity in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
985
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
569
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
679
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock