Discuss High integrity earthing in the UK Electrical Forum area at ElectriciansForums.net

Zdb

-
Esteemed
Reaction score
496
Only time I've done this has been using the two separate CPCs of a RFC using different terminals inside the D.B as per 543.7.1.204

I've been asked to test a load of high integrity radial circuits with two separate (different sized) CPCs.

My question is, in the box which asks for the CSA of the CPC, do you just write that of the radial and make a note of the other size in the comments or do you add the two CSAs together.

My initial thought was add them together but then I thought we dont write 3mm when installing a 2.5/1.5 RFC.

Any advice welcomed
 
Only time I've done this has been using the two separate CPCs of a RFC using different terminals inside the D.B as per 543.7.1.204

I've been asked to test a load of high integrity radial circuits with two separate (different sized) CPCs.

My question is, in the box which asks for the CSA of the CPC, do you just write that of the radial and make a note of the other size in the comments or do you add the two CSAs together.

My initial thought was add them together but then I thought we dont write 3mm when installing a 2.5/1.5 RFC.

Any advice welcomed
That would be 4mm wouldn't it?
 
I would more than likely add them together and make a note on the cert reflecting the amount of cables on the circuit.
 
That would be 4mm wouldn't it?
I think Pete is correct there being a minimum of 4mm single earth when protected against mechanical damage.
If you are saying you have a 2.5/1.5 radial with a 2.5mm earth from the end of the radial to the distribution board I would put down 1.5 as the circuit CPC. What is the installation method?
 
Only time I've done this has been using the two separate CPCs of a RFC using different terminals inside the D.B as per 543.7.1.204

I've been asked to test a load of high integrity radial circuits with two separate (different sized) CPCs.

My question is, in the box which asks for the CSA of the CPC, do you just write that of the radial and make a note of the other size in the comments or do you add the two CSAs together.

My initial thought was add them together but then I thought we dont write 3mm when installing a 2.5/1.5 RFC.

Any advice welcomed
Because that’s just one conductor.
 
That would be 4mm wouldn't it?
I think he is referring to the 1.5/1.5 of a ring final circuit. It depends on the schedule format you are using and whether you can insert all conductor csa. I like to include all as I hand write them so if you have a 2.5 T&E with a separate 4mm cpc I would put 1.5/4.0
 

Reply to High integrity earthing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
Replies
19
Views
3K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock