I have been asked to remove a 3 ph rcd from a vehicle entry gate, because they state it has an inverter power supply that can leak up to 160 ma .

this does not seem correct to me and i wonder of the implications of having no rcd if this leakage is to earth on touchable large metal gates.

any thoughts?
 
I would not do it. Let the people who are installing the inverter do it. If they are installing equipment that means compromising safety then they should take the risks associated with that.
 
why Is the rcd required?
and an extra word.
For additional protection i would imagine, the rcd is already existing , the company i work for has subbed the job to another company , who have asked us to remove the rcd due to likely tripping issues.
i wonder if a type B rcd would solve the problem?
the manual for the omron 3gmx2 mentions dual independent earths so its clearly a problem ,this supply also supplies 3 lifts and water pumps ,metal conduit to metal light switches on so on.
 
If I have the right product, the manual also says:

Use an earth leakage breaker for circuit (wiring) protection between the power
supply and the main power supply terminals (R/L1, S/L2, T/L3).
An earth leakage breaker may malfunction at high frequencies as those generated
by an inverter. Use an earth leakage breaker with a large high-frequency
sensitive current rating.
When sensitivity of 30mA or even less earth leakage maybe required in certain
applications (e.g. domestic), short motor cable and convenient low-leakage
EMC filters should be selected. Check with your supplier for additional
indications.
It looks like not having one at all isn't an option.
As you said, selecting the right one seems to be the way forwards and I wouldn't be scared to phone them up and ask for advice.
 
I've just also noticed this bit:
1657205288997.png
 
For additional protection i would imagine, the rcd is already existing
Is "additional protection" actually needed?

If it is hard wired and using SWA or similar (i.e. no vulnerable buried cables near the surface) then I don't see any requirement for a RCD, other than high Zs in a TT case. More so if you have a CPC in the SWA as well, so dual earth paths (armour and copper CPC).
 
I think additional protection is absolutely required , we know it may leak up to 160ma ,possible not all at 50hz it seems the manufacturers talk about special gfci which is an rcd by another name,it seems reckless to me to knowingly pass current down a cpc/earth
 
I think additional protection is absolutely required , we know it may leak up to 160ma ,possible not all at 50hz it seems the manufacturers talk about special gfci which is an rcd by another name,it seems reckless to me to knowingly pass current down a cpc/earth
Almost all devices pass some current down the CPC, might be microamps, might be milliamps, might even be amps if you have a big enough installation. That is why RCDs come with all sort of trip thresholds depending on what they are protecting, with the fancy MCCB incomer types often being adjustable from 30mA to 5A or more, and delays from "none" to typically 1 second or more..

For sockets with high leakage current there is/was a recommendation in the regs for dual CPC so no single point of failure in the earthing arrangement to combat the risk of an open CPC under "normal" conditions, let alone having a L-E fault at the same time.

Here you could run a 2nd CPC in parallel with the feed cable if that risk is a concern. However, I would start by looking at how it is installed and if the existing arrangement looks reliable and is not in need of "additional protection" for and cable damage contact.

.
 

Reply to High leakage equipment? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Got a jolt from the metal frame of my 2020 Sony KD-65X9000H TV. Measuring 120VAC at all times unit is plugged in. Now I know there's often some...
Replies
8
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
915
Afternoon all, I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock