High R1&R2 readings

Discuss High R1&R2 readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

So as this is a lollipop circuit, out of interest i imagine the ring part of the circuit still needs the standard tests applied as you normally would carry out?

A 40amp ocpd is surely not suitable?
Well the OCPD needs to be able to protect the cable, it may or maynot be okay, a 20 or 32 would be the choice of many I am sure, what we need from the OP is the following 3 ansers to the 3 questions below

(1) how did you measure the ZE
(2) are you 100% sure the ZS was at the furthest point on the circuit
(3) Have you inspected the JB to see if all conductors are tight.
 
So as this is a lollipop circuit, out of interest i imagine the ring part of the circuit still needs the standard tests applied as you normally would carry out?

A 40amp ocpd is surely not suitable?

I've got a few years experience under my belt, but, I've never heard of a lollipop circuit before. Are these common to you?
 
1. Probably did not null his leads to have an R1 + R2 that high bearing in mind Zs, or more likely, just can't test and god knows what he is referring to.
2. More interesting is the 40A RCBO on his 2.5mm RFC
 
Last edited:
I've got a few years experience under my belt, but, I've never heard of a lollipop circuit before. Are these common to you?

There are lots about..."kitchen fitters" love to adapt an old VIR cooker/water heater feeds,for their little ring + off-shoots...time to select "sanity",on the MFT...:blush5:
 

Reply to High R1&R2 readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock