Discuss High ZE Reading in Flat in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
I have been asked to carry out a rewire of a top floor flat when checking the existing supply characteristics.
TN-S with a ZE of 1.24 ohms and PFC of 1.91 KA. 1361 Type 2 with 100 amp Fuse

Should I contact the DNO and ask for them to come and check before commencing work.
Unable to treat as TT and run earth cable down the back of the building, will be using a Wylex dual RCD board for all circuits.
If I complete a certificate all my Zs reading will be really high.
 
Yes that ze is far too high, should be about 0.8 for a tns system. Contact dno and ask if a tncs upgrade is available, otherwise no choice but to convert to tt.
Could be that the dno have not provided an earth for that installation.
 
Last edited:
Think you NEED to answer Jeremy's question first, BEFORE you go calling the DNO!!!


Is the origin of the supply in the flat or in a communal meter cupboard downstairs?

The way i'm reading your OP, is that your taking your Ze test readings from the flat's CU which isn't Ze at all, but Zs, and you should be leaving all earthing and bonding conductors in place for a true Zs reading. Taking Zs at the sub-main CU, is commonly called Zdb...
 
Last edited by a moderator:

Reply to High ZE Reading in Flat in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
I've just finished an installation on a large outhouse around 50 meters from the main property, but I'm having issues with unusually high Zs...
Replies
11
Views
4K
Hi knowledgeable collective. To the chase. TN-S Megger 1553 2 wire Ze 0.09 but was getting Zs on cooker cable 1.5 metre long using No trip 3...
Replies
8
Views
995
Hi all, Hope you are all well. I went to do an EICR at a small domestic property supplied by a TN S today, it is wired in singles using the...
Replies
29
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock