Yes you can give some leeway but if your cpcs are 1.5/1.5 then your reading is way above what it should be.
Discuss High Zs reading in the UK Electrical Forum area at ElectriciansForums.net
Should I be looking for Anything other than a loose connection ?Yes you can give some leeway but if your cpcs are 1.5/1.5 then your reading is way above what it should be.
I think I should look again for the loose connection on the CPC, I’m pretty sure the cable is 2.5-1.5.
does the result have to be within 1.67 or is it allowed to be slightly over? I was told 1.67 is what we would expect to see so when would you start to look into it?
Had two circuits like this couple of weeks ago and both were terminal screws on the green/yellow sleeving and not the conductor.Should I be looking for Anything other than a loose connection ?
If the fused spur was on Cct 4 say, then I put it under that as Cct 4A and put a short explanation in the note section.Excellent. Would you write that result on the test form and mention the fuse spur somewhere? Thank you