Discuss hmo wiring advice in the Commercial Electrical Advice area at ElectriciansForums.net

dougquade

DIY
Reaction score
0
Hi My mate has purchased a house which is being converted into multiple occupancy (8 rooms). Unfortunately the spark passed away halfway through the job. each room has been fitted with a 2 way CU with 16a+6 breaker fed via a 4mm cable. He installed double stacked hager board with 2 main 100a breakers, kitchen and communal all on rcbos (top section) and all rooms feeds on 20a mcbs (bottom) section. The board has been fed via 25mm swa (extended)

Now is this the right way to do it? will 4mm be enough to handle the load and is connecting 8 x 4mm room loads + kitchen on one board be enough?

Thanks

Doug

ps I’m a Apprentice btw
 
Without seeing the job, the sizing sounds ok. (depends on how the house is heated though, and cooker and shower facilities)
The main thing to say is that your mate will need to get another electrician involved sooner rather than later, one that will take responsibility for the previous sparks work up to now. (ASAP, so they can see the cable routes etc)

The council will need an electrician who is a member of a scheme to sign it off before they give an HMO license.


Doug Quade.... That would be Arnies character in Total Recall?
 
House is heated via gas boiler same with the showers. Gas hob and electric oven. The 4mm cables are T&E not swa. I would say they run through some insulation though. maximum runs of 18m.
 
We can't comment on whether the installation is compliant so far or not without seeing it.... but any electrician taking on a half finished job needs to know 100% so they can sign it off.
Unfortunate situation
 
We can't comment on whether the installation is compliant so far or not without seeing it.... but any electrician taking on a half finished job needs to know 100% so they can sign it off.
Unfortunate situation
There’s no mention of the fire alarm and emergency lighting, I would have installed minimum 6mm it’s probably cheaper that 4mm, it’s certainly better have that security of extra capacity
 

Reply to hmo wiring advice in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock