Search the forum,

Discuss Hob and hood on same circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi There, I am hiring an electrician shortly but so far have received conflicting advice so looking for clarity before I spend my money.

Can a socket for a kitchen self circulating hood and under cabinet lights be on same circuit as hob according to UK regulations?

Any advice appreciated.
 
I can't see why this would be a problem providing it is sized for it and meets the requirements for ADS. I would personally want the hood on a fused spur and it will most likely be required in the manufactures literature. How are the cabinet lights going to be controlled?
 
I can't see why this would be a problem providing it is sized for it and meets the requirements for ADS. I would personally want the hood on a fused spur and it will most likely be required in the manufactures literature. How are the cabinet lights going to be controlled?
Thanks for reply. The hood is quite small as it's a very small kitchen.

Bearing in mind I have vary little electrical knowledge, in a nutshell: There's already a vertical lead for the hood/light socket which is connected to the hob outlet (Installed by previous owner). There's also an isolator switch at a different location.

The cabinet lights are from Ikea which has some kind of transformer which will be plugged into the socket and can be switched on and off with a wireless dimmer.
 
You can have one double socket off a radial without a spur. Usually, that would be wired in 2.5mm cable.

If you protect it with a fused spur with a 13A fuse then you can have a load up to the fuse rating and only need 1.5mm cable, I don't think you are going to care if the circuit trips before the fuse blows so you wouldn't need to worry about coordinating the devices.
 
You can have one double socket off a radial without a spur. Usually, that would be wired in 2.5mm cable.

If you protect it with a fused spur with a 13A fuse then you can have a load up to the fuse rating and only need 1.5mm cable, I don't think you are going to care if the circuit trips before the fuse blows so you wouldn't need to worry about coordinating the devices.

Given my lack of expertise with this stuff I better leave it with my electrician but really happy that it all seems doable without too much hassle so thanks for the input. Much appreciated.
 
Given my lack of expertise with this stuff I better leave it with my electrician but really happy that it all seems doable without too much hassle so thanks for the input. Much appreciated.

Strange how I still seem to get conflicting advice from qualified electricians 🥴, wonder if anyone can shed some light on this before hiring.

As mentioned above we need to get a socket installed in kitchen. At the moment there's a lead available which is connected vertically to a hardwired socket. The cable used for the socket is 6mm cable. The vertical cable for the new socket is 2.5 mm.

The advice I've had is the 2.5 mm cable needs to be changed to 6 mm. Is that correct advice?

Many thanks
 
Last edited:
No harm, but equally no point, if its just to a single socket point. The maximum demand from a 13A double socket is 20A, which is within the capacity of 2.5mm2.
Should add to my last post "and the hob circuit is protected by a 30mA RCD".
 

Reply to Hob and hood on same circuit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock