Discuss Wiring new Hob / Cooker into circuit in the UK Electrical Forum area at ElectriciansForums.net

joshimoto

DIY
Reaction score
0
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units). Max draw 3.5kW and 7kW respectively. I believe the circuit is radial from consumer unit (32A RCD) to 45A DP switch plus socket. Have done diversity calcs and got 25.125A which seems sufficient for the switch. Looking at the cable it seems to be 6242Y 2x10+4 mm to and from the switch over about 18m or so, runs through roof space and down behind plaster wall.

However, at some point in the past the cable has been cut, then joined to 2.5 t&e in a connector box with 3 double sockets spurred off, as well as a fused switch to an external oil boiler through the wall outside. All of this seems to be on the cooker circuit - i.e. switching off the cooker switch isolates all of the above. I've got the impression this doesn't seem right and am looking at ways of rectifying for safety. As I say above, most likely will get in a qualified electrician, but the 2.5mm spurs and boiler connection are giving me concern. Looking at fitting FCUs or a Dual cooker connection unit to the appliances as they'll both be hard wired. Any advice greatly appreciated :)
 
If multiple socket outlets are connected via one length of 2.5mmsq then it is not protected against overload by the 32A device in the CU. (You mentioned an RCD but I guess you mean RCBO, or MCB, as an RCD doesn't provide overload protection.) If each point has its own 2.5 back to the junction with the 10.0 then they can't readily be overloaded and they are probably OK for short-circuit protection, but it's a non-standard configuration that would be hard to defend. Plus, you need most of that circuit's capacity for the oven and hob.

The cooker isolator should also be exactly that; one does not want to be 'hesitant' to isolate a dangerous situation or over concern that the heating boiler will also go off. If your new oven turns out to have moisture in the elements that causes RCD nuisance tripping, again you need to be able to isolate it individually.

So it fails on two or three accounts. Solutions might include running a 20A radial out to meet the orphaned sockets, breaking them into an existing ring if present, or turning them into a fused spur with a fused connection unit spurred of the existing ring, which is something of a last resort in a kitchen as the 13A fuse is a limiting factor and likely to get blown if the sockets are heavily used. If you were running a new cable, there is something to be said for running two and separating the heating supply entirely.

Re. the job you actually wanted to do in the first place i.e. connect the oven and hob, double-check that the oven instructions don't specify a 20A (Max) fuse. No FCU's for either of these as they are both over 13A.
 

Reply to Wiring new Hob / Cooker into circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
722
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
805
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
619
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
829

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock