Think I’m missing something here. Have been asked to remove a Horstmann E7 BX and replace with an Electronic 7.

The existing set up is two immersion elements (top & bottom) in one cylinder, 24hr top and O/P bottom

Now, the BX has connections for both the incoming off peak and 24hr supplies, likewise outputs, but the Electronic 7 only has one set of terminals for the incoming supply (L/N), and separate outputs for off peak and 24hr supplies. The spec says it’s suitable for two immersion elements.

Surely both O/P and 24hr supplies do not go into the same terminals???!
Any advice?
 
Ok, now clarified. The Electronic 7 can only be used on a two rate meter, not on a two meter supply (which is what I’m dealing with).
There apparently isn’t a suitable programmer for this setup, to do what my customer wants - limit the time the off peak charge is taken.
 

Reply to Horstmann Electronic 7 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The unit only heats water using the programmed boost and when pressed in the 1 2 or Cont boost function. I have checked the off-peak time which...
Replies
7
Views
382
I have two supplies into a new horstman e7 box, 1 from the offpeak water heating one from standard tariff boost do both suppies go to 1 and 2, 4...
Replies
3
Views
583
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
576
Hi All, I have been having an odd issue with My Horstmann Electronic 7. It had been working normally and then I found that the display had turned...
Replies
10
Views
4K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock