Discuss Hot Water cylinder and 2x immersion heaters in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
17
Apprentice electrician (coming towards the end of my 1st year) here and looking for some help and understanding.

I have moved into my flat and I have both a normal CU running 24/7 and an off peak CU.

The flat has no gas and all electric. I have a hot water cylinder which has 2 immersion heaters in it. One near the top and one near the bottom. I am guessing the bottom one is the economy one which only comes on at night and the top one is for when I hit the boost button?

The controller is in the kitchen which is a horstmann economy 7 quartz. This then goes to a single FCU which has 2x 1.5mm flex's in it, one for the top and one for the bottom heater. FCU is fed by a 2.5mm cable.

The 13amp fuse is has blown. I tried changing it and it blew again, then the MCB, 16amp tripped also. On making sure all the connections were ok, every cable was very hot. The new cylinder was installed in November last year apparently.

Now I have no hot water what so ever.

Should the economy heater not be on its on supply from off peak CU? Am I better rewiring this? Off peak CU to off peak heaters via a 20amp double pole switch and a new supply from the 24/7 CU to a FCU, to a controller then to the top heater?

Cheers.
 
Are you sure you havnt already played with it? The 2 immersions should wire back to the horstmann seperately so they dont run together otherwise yes you will pop fuses because its trying to draw 6kw on a 13A fuse
 
Apprentice electrician (coming towards the end of my 1st year) here and looking for some help and understanding.

I have moved into my flat and I have both a normal CU running 24/7 and an off peak CU.

The flat has no gas and all electric. I have a hot water cylinder which has 2 immersion heaters in it. One near the top and one near the bottom. I am guessing the bottom one is the economy one which only comes on at night and the top one is for when I hit the boost button?

The controller is in the kitchen which is a horstmann economy 7 quartz. This then goes to a single FCU which has 2x 1.5mm flex's in it, one for the top and one for the bottom heater. FCU is fed by a 2.5mm cable.

The 13amp fuse is has blown. I tried changing it and it blew again, then the MCB, 16amp tripped also. On making sure all the connections were ok, every cable was very hot. The new cylinder was installed in November last year apparently.

Now I have no hot water what so ever.

Should the economy heater not be on its on supply from off peak CU? Am I better rewiring this? Off peak CU to off peak heaters via a 20amp double pole switch and a new supply from the 24/7 CU to a FCU, to a controller then to the top heater?

Cheers.

Have you meggared the element to earth to see if it is down, this is the answer 90% of the time.
 
I'm not sure about your off-peak systems, I'm not in the UK. Maybe one of the members closer to you has some info on this.

Does thew tripping happen instantaneously or is it after a short period of time?

If your elements were working fine and now they're tripping / blowing fuses I'd suggest you first trace the fault. Isolate power, test for dead, disconnect both elements, visual check for leaks, IR test, continuity test elements and same again for the wiring. Sometimes faulty element tubes don't show up very well on tests and it might be necessary to drain and remove elements to properly visually check them for cracks or splits.
 
I haven't played with it cause I wasn't sure.
Are you sure you havnt already played with it? The 2 immersions should wire back to the horstmann seperately so they dont run together otherwise yes you will pop fuses because its trying to draw 6kw on a 13A fuse

No played with anything. Only thing I have touched is changing the fuse. It is a single 2.5 t+e feeding the fcu with both elements being feed from it. Also took out the 2 flex's and IR tested them.

Surely it would have blowing the second it was all installed and used by the previous owner?
Have you meggared the element to earth to see if it is down, this is the answer 90% of the time.

Took out the 2 flex's and IR tested them. Both came back with over 50mohms.
 
I haven't played with it cause I wasn't sure.


No played with anything. Only thing I have touched is changing the fuse. It is a single 2.5 t+e feeding the fcu with both elements being feed from it. Also took out the 2 flex's and IR tested them.

Surely it would have blowing the second it was all installed and used by the previous owner?


Took out the 2 flex's and IR tested them. Both came back with over 50mohms.
took the flexs out from the element or the timeclocks?
 
If the bottom element is on the off peak CU then i would see if it is labelled, but generally the E7Q timer works on the normal rate tariff and timer turns the bottom element on and the boost button turns the top element on.
1 of the immersions is faulty (probably the lower one) but with out testing with the correct tester (insulation/multifunction tester) you will not know for sure.
It does seem strange that 2 flexes are connected in the same fused spur, there should be a fused spur which feeds the E7Q and then both immersions should be connected in the correct places in the E7Q so both cannot be switched on at the same time
 
took the flexs out from the element or the timeclocks?
There's only one time clock which is in the kitchen.

Both elements go back to a single FCU which is fed from the controller. I took both flex's out of the FCU which go into both elements. I IR'd them from the disconnected FCU side.
 
Hmm, Something doesn't sound right to me, unless I am missing something, ashrow above has posted what I was thinking so I am a little confused to be honest.
 
If the bottom element is on the off peak CU then i would see if it is labelled, but generally the E7Q timer works on the normal rate tariff and timer turns the bottom element on and the boost button turns the top element on.
1 of the immersions is faulty (probably the lower one) but with out testing with the correct tester (insulation/multifunction tester) you will not know for sure.
It does seem strange that 2 flexes are connected in the same fused spur, there should be a fused spur which feeds the E7Q and then both immersions should be connected in the correct places in the E7Q so both cannot be switched on at the same time

No sorry. Both elements are on the 24/7 supply. Neither is on the off peak supply.

It leaves the 24/7 CU via a 16amp MCB, goes to the timer, then from there goes to a FCU via a 2.5 t+e, then from there both flex's go to both element's.
 
well each element is 3KW which is 13 amps, so 1 16 amp breaker will trip won't it?
 
The norm set up with 2 elements is, off peak and 24 hour .
Should it not be installed like this? ... Well at least, that's how I thought it should be done.
kl1aqLQ.png
 
I agree. But it's not done this before. Everything has worked before with no issues.

Would I not be better just rewiring the whole thing and making a better job?
well certainely each element needs its own FCU and MCB, so yes get stuck in.
 

Reply to Hot Water cylinder and 2x immersion heaters in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The unit only heats water using the programmed boost and when pressed in the 1 2 or Cont boost function. I have checked the off-peak time which...
Replies
7
Views
408
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
232
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
894
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock