Discuss Hot Water cylinder and 2x immersion heaters in the UK Electrical Forum area at ElectriciansForums.net

If both elements were running together it would take several minutes for a 16A MCB to trip at 26A load and highly unlikely that the fuse and circuit breaker would both trip together.
 
well certainely each element needs its own FCU and MCB, so yes get stuck in.
I will rewire it myself and then get someone from work to double check for me. I get I'm an apprentice, but gota learn some how. Thanks for your help.

Thanks for your help. Will do this.

Well in that case it can never have worked for any length of time as it's trying to draw 6kW through a 13a fuse !
I did kinda think someone was taking the p**s outa me. I will rewire it properly.

Thanks for your help guys. Was kinda embarrassed to ask for help from the guys from work in case they torn me a new one rather than help.
 
This needs sorting out as a matter of urgency, Shermin with all due respect I'd ask the Sparks that you're training with to have a look with you so you then understand with some confidence what needs doing.
Yeah I will do. Will rewire it myself and then get someone to check it out. But I take it from the pic above, that is the correct way?
 
Yes the drawing is good apart from if there are two separate supplies I see no need for the boost controller or 'Control Board' as you'd have two individual supplies to two elements via independent 20a DP switches. If it's a pain to run a 2nd 2.5 from mains position you could fit a Horstmann or similar controller in the airing cupboard, the timed output is designed to coordinate with E7 times and the 'boost' function connects to the top element - all designed so both can't be energised at the same time.
 
It doesn't need rewiring unless the supply cable is up the swanny. A single supply from the peak board should go to the SFCU/DP switch, from the load side of the SFCU/DP switch is then connected to the LNE terminals of the controller, the bottom immersion is then connected to terminal 5 and the top immersion is connected to terminal 4. You set the off peak time on the controller which controls the bottom immersion and the boost function controls the top immersion. Unless the controller is faulty then it's impossible to turn on both immersions at the same time, hence limiting the load to 3KW/13A. Measure the impedance of the immersions, IR the immersions and check the controller is functioning correctly.
 
I will rewire it myself and then get someone from work to double check for me. I get I'm an apprentice, but gota learn some how. Thanks for your help.


Thanks for your help. Will do this.


I did kinda think someone was taking the p**s outa me. I will rewire it properly.

Thanks for your help guys. Was kinda embarrassed to ask for help from the guys from work in case they torn me a new one rather than help.


It shouldn't be that way, I always say to my son [and apprentice], never ever be afraid to ask anything even if you think it's trivial. With you still in your 1st year especially I'm not impressed by the sound of your 'mentors'.
 
Yes the drawing is good apart from if there are two separate supplies I see no need for the boost controller or 'Control Board' as you'd have two individual supplies to two elements via independent 20a DP switches. If it's a pain to run a 2nd 2.5 from mains position you could fit a Horstmann or similar controller in the airing cupboard, the timed output is designed to coordinate with E7 times and the 'boost' function connects to the top element - all designed so both can't be energised at the same time.
The CU's are in the same cupboard next to the cylinder. About 3 metres apart.
 
Sounds to me as if the controller has given up the ghost..............

Best you find the installation wiring instructions as I believe this unit relies on its own internal "clock" to switch to the lower element ....... ........ so if they are both working together its certainly not correct.
 
The only place nearby to me that will sell anything readily available is screwfix.

Will this be ok?

https://www.NoLinkingToThis/p/lap-7-day-digital-immersion-timer/1804r
 
So if I take a supply from the 24/7 supply board, to a FCU, then to the controller, then take a separate cable to each element all should be good?

I'd ditch the FCU and use a 20a DP switch, you have adequate overcurrent and short circuit protection with the 16a MCB, the DP switch is more suited to the load than a 13a fuse constantly running at full current.
 

Reply to Hot Water cylinder and 2x immersion heaters in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The unit only heats water using the programmed boost and when pressed in the 1 2 or Cont boost function. I have checked the off-peak time which...
Replies
7
Views
391
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
229
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
878
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock