Hi,
I have to quote to provide a circuit for a hot tub outside. Could you let me know if what I plan to do sounds okay?

So from a 30ma RCD and 40A mcb there is an existing 10mm2 twin and earth going to the garden through conduit approx 20mtrs from the board. It is PME system. From there I had planned to install a rotary isolator 2 mtr from the tub, some 6mm2 swa to the terminals. The hot tub can draw 12.6kW.

I really appreciate your help.

thanks
 
well could draw 55A and you using 40A mcb.. can you get mabufactures instructions... but if you have 40A mcb will protect cable,and hope doest be on for hours..... you should be fine

- - - Updated - - -

maybe a c breaker
 
Hi,
I have to quote to provide a circuit for a hot tub outside. Could you let me know if what I plan to do sounds okay?

So from a 30ma RCD and 40A mcb there is an existing 10mm2 twin and earth going to the garden through conduit approx 20mtrs from the board. It is PME system. From there I had planned to install a rotary isolator 2 mtr from the tub, some 6mm2 swa to the terminals. The hot tub can draw 12.6kW.

I really appreciate your help.

thanks

Your PME supply could well be a problem with an outdoor hot tub installation. Look at the bottom of this page for ''Tags for this thread'' and click on Tubs. I'm sure you'll find everything you'll need to know on installing an outdoor hot tub from these listed threads. If not, then come back with any queries you may still have....
 

Reply to hottub help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have someone that wants a hot tub installing and it’ll be my first time, I have came up with anxixeaxfwanted to check it was correct. I wanted...
Replies
10
Views
1K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
674
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Replies
7
Views
2K
Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock