Hi all,
just wanting some thoughts on this topic. i'm getting some very random blinks from a couple of downstairs lights. i changed most of my bulbs to LED, and from browsing it seems they're a lot more susceptible to current fluctuations etc, there has been one incident when a normal filament dimmed for a second or two but aside from one genuine power cut to the area the only issue is the blinks. it's totally random, no pattern - can be days between them; the light will blink once usually, and that's it. i've read that neighbouring properties' usage can cause fluctuations etc and i'm thinking it might just be the incoming supply, what w/ the colder/darker nights prompting more lights/heaters etc. i've had the tv and other things on when a blink has happened, they don't seem to be affected. also, the blinks don't happen when i do stuff, switch the kettle on or of etc.

is it something i'm just going to have to live w/?

TIA
 
could be caused by phantom voltages on LEDs. cure is called a snubber, fitted across L and N of the affected lights.
 
Hi all,
just wanting some thoughts on this topic. i'm getting some very random blinks from a couple of downstairs lights. i changed most of my bulbs to LED, and from browsing it seems they're a lot more susceptible to current fluctuations etc, there has been one incident when a normal filament dimmed for a second or two but aside from one genuine power cut to the area the only issue is the blinks. it's totally random, no pattern - can be days between them; the light will blink once usually, and that's it. i've read that neighbouring properties' usage can cause fluctuations etc and i'm thinking it might just be the incoming supply, what w/ the colder/darker nights prompting more lights/heaters etc. i've had the tv and other things on when a blink has happened, they don't seem to be affected. also, the blinks don't happen when i do stuff, switch the kettle on or of etc.

is it something i'm just going to have to live w/?

TIA
I had a similar problem recently
stuck my meter across the supply and it was around 170Volts
I contacted the supply company, first bloke said now wrong, didnt do much testing and buzzed off
problem kept happening
got them back showed a picture of the meter readings
turned out to be the cut out blades either worn or corroded, recently had a smart meter fitted and I was worried that was causing it
they dropped a new fuse in after cleaning and tightening the blades and connector screws
all seems good now
you might have an electrical surge though from another property on the same phase, any one had an electric car charger installed recently ?
 
hi,

thanks for the replies. not sure about the neighbours' cars, to be honest. Given the issue doesn't affect anything but the lights, it seems, it might just be me being paranoid, our phase does seem to be a bit cursed though, a couple years back it went out for almost a full day, and in 2019 i had over 4 months of long periods of light flickers that i had the suppliers out over countless times; they said part of the supply was giving up and was hard to tell where the fault was until it actually gave up, which it eventually did on new year's eve started off just making the lights flicker badly then got to the point where my computer fans started to labour when it happened and i was getting very jittery about damage etc. Think it's left me w/ an ingrained nervousness/panic when i get the odd blink :-D
 

Reply to House Lights - Random Blinks. in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I am adding a light fixture in a room I am restoring in my 160 yo house. I have ran a new 12-2 w/ground wire from the ceiling box to a junction...
Replies
2
Views
882
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
700
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
684
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
319

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock