Discuss How are max circuit lengths calculated in table 7.1 in the UK Electrical Forum area at ElectriciansForums.net

n180

-
Reaction score
23
Something I'm not quite getting.

In table 7.1(i) of onsite guide the max circuit length of (for example) a lighting circuit on 6 amps, with rcbo and wired in 1.5mm is 106 meters.

Where does this 106 meters come from because if max volt drop allowed is only 3% for lighting, 106m works out to 8% volt drop?

same sort of case for ring circuits.

What am I missing?
 
For lighting circuits it assumes an evenly distributed load where the average current is half the total load current (Ib goes from 6 amp as is the mcb to 3 amp) so 3 amps is used in the calculations and not 6 amps.
Of course the on site guide gives the most onerous results, you don’t need to take them as gospel as your loading thus calculations maybe totally different giving you more length or sometimes less than what’s given in the on site guide.
Limiting VD can be given as
6.9 X 1000/ Ib/2 X ( mV/A/m)
 
Last edited:
Thanks, I didn't realise Ib can be divided by 2 in the calcs.

So for any circuit we design we can claim even distributed load by dividing any Ib by 2?
 
Thanks, I didn't realise Ib can be divided by 2 in the calcs.

So for any circuit we design we can claim even distributed load by dividing any Ib by 2?
Generally it’s limited to lighting circuits as the load isn’t all lumped at the extremity of the circuit and the loads to each luminaries are generally even ie similar sized lamps used or the actual individual lighting loads are negligible unlike say a radial socket circuit where anything upto 13 amps could be plugged into a individual outlet or a fixed load radial like a shower.
 

Reply to How are max circuit lengths calculated in table 7.1 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Hi I'm looking at Table 7.1(i) in the On Site Guide. Max length of cable runs. In some cases where there is no RCD protection the length is...
Replies
4
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
799
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock