Assuming that you measure the windings for a power transformer, for example:
A-B: 2,258 ohms
B-C: 2,262 ohms
A-C: 2,250 ohms, how do you calculate the tolerances for these? What formula do you use? You consider as reference the highest or the lowest value from every 2 readings?
I just wanna check an industry tollerance of +/- 5%.
Thanks.
 
Are these dc resistance measurements?

Assuming for now they are then:

1. Find the mean average of the resistances of the three windings. Thus Rmean = (2258 + 2262 + 2250) / 3;

2. Find the percentage difference D of each winding resistance from Rmean. Thus for example for the first winding

D1 = (2258 - Rmean) x 100 / Rmean

3. Now compare D1, D2 and D3 to +/- 5%
 

Reply to How do you calculate the tollerances from a 3 phase winding measurement in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
759
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
Replies
17
Views
3K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock