Hi everyone first post here as I need some advice and can't work it out.
I have only 1 double socket by a new desk area, I will have around 7 appliances on an extension cable but never used at the same time.
I can calculate how much will be being used at maximum comes in around 5amps, apart from one appliance.
It's a guitar amp processor with the specs below.
How do I use this data to calculate how many amps the powerhead/powerRack will use?
Thanks for any help
Screenshot_20210302_191908.jpg
 
think the 10A is a max. value. a double socket is rated at 20A for both outlets together. why not add (or get local electrician to add) another double socket next to existing.
 
If it is rated 10A max with voltages in the range 100-125 or 190-245, the maximum power input will be 10 x 100 = 1000W. At 230V this would be 1000 / 230 = 4.3A

But an audio power amplifier only normally uses a fraction of its maximum rated power, except for momentary peaks which have little impact on the electrical supply rating. I would expect it will idle along at 1A or so, occasionally peaking at a couple of amps.

The Kemper powerhead is rated at 600 Watts.
So at 190 volts it would draw 3.15 amps. At 230 volts it would draw 2.6 amps.
The 600W is the output power, so it will require more input than 600W. I suspect it's a class D (switching) amp so maybe 700W input, which allowing for power factor might be 800VA, or a bit over 3A at 230V. If it were a linear amp it would require more. The class A amp I am listening to at the moment takes 150W from the mains to produce 20W of audio.

But, there are lies, damn lies and power ratings. It claims 600W RMS into 8Ω speaker load. That's sqrt (600/8) = 8.7A supposed to come out of the 1/4" output jack. That would melt most jacks if you played a 600W continuous tone through them. Thankfully most music requires only 1% or so of rated power except for the peaks.

So yeah, an amp, peaking at a couple of amps. Amp as in Ampère, not amplifier.
 
If it is rated 10A max with voltages in the range 100-125 or 190-245, the maximum power input will be 10 x 100 = 1000W. At 230V this would be 1000 / 230 = 4.3A

But an audio power amplifier only normally uses a fraction of its maximum rated power, except for momentary peaks which have little impact on the electrical supply rating. I would expect it will idle along at 1A or so, occasionally peaking at a couple of amps.


The 600W is the output power, so it will require more input than 600W. I suspect it's a class D (switching) amp so maybe 700W input, which allowing for power factor might be 800VA, or a bit over 3A at 230V. If it were a linear amp it would require more. The class A amp I am listening to at the moment takes 150W from the mains to produce 20W of audio.

But, there are lies, damn lies and power ratings. It claims 600W RMS into 8Ω speaker load. That's sqrt (600/8) = 8.7A supposed to come out of the 1/4" output jack. That would melt most jacks if you played a 600W continuous tone through them. Thankfully most music requires only 1% or so of rated power except for the peaks.

So yeah, an amp, peaking at a couple of amps. Amp as in Ampère, not amplifier.
I knew you'd be along to amplify the detail!
 
I like to keep the forum's signal-to-noise ratio as high as possible and minimise distortion. Some might see my constant impedance as a damping factor, but apart from occasional intermodulation I think between us we achieve impressively high fidelity.
 

Reply to How many amps would this draw? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone! I have a question regarding the electricity supply and the maximum demand. One energy utility supplies an 18 kVA maximum...
Replies
10
Views
2K
Hi Forum Members I have a 4 pole single phase 240VAC 315 watt motor from a central heating heating system that I think is bad. It's the room fan...
Replies
18
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
506
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
938

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock