Discuss How to add ~25kw to garden? in the UK Electrical Forum area at ElectriciansForums.net

anthony_0

DIY
Reaction score
0
Hi all, we're renovating our property and looking to install a sauna (7kw), electric shower (9kw), outdoor heater (4kw), small lights (200w) and an electric point for things like a lawn mower. In total, I was estimating around 22kw if we had all devices on with no diversity. The current fuse box in the basement is getting quite full and in the future we're planning to put a car charger in that one which I imagine would be 7kw-9kw. Would it make sense to put another fuse box in the garden and run a 10mm cable from the one in the basement to the one in the garden? I think the cable running from the main road into the house is only 16mm? The overall distance between the two fuse boxes would be 22 meters. The cable would be running through a 32mm conduit buried under the concrete. The main thing I'm thinking is that if I switched on everything in our house such as lights, induction hob, ovens, sockets, and everything in the garden mentioned above, etc, it would come to a total of 76k for the overall house. Many thanks in advance.
 
You really should get a professional electrician involved for this.

Not only as it falls within Part P of the England and Wales building regulations so is notifiable work, but the sort of loads you are talking about potentially exceed the typically 80A domestic supply capability by a large amount and you might need to look at other demand control means or even an upgrade to a 3-phase supply with significant related changes to your CU (consumer unit / fuse box / distribution board).

76kVA is 330A at 230V after all!
 
You really should get a professional electrician involved for this.

Not only as it falls within Part P of the England and Wales building regulations so is notifiable work, but the sort of loads you are talking about potentially exceed the typically 80A domestic supply capability by a large amount and you might need to look at other demand control means or even an upgrade to a 3-phase supply with significant related changes to your CU (consumer unit / fuse box / distribution board).

76kVA is 330A at 230V after all!
Thanks, I understand that I'll need a professional for the installation and this isn't something I would attempt myself. I'm looking to hear a couple of views on the actual installation though so I can at least understand what would be required.
 
Thanks, I understand that I'll need a professional for the installation and this isn't something I would attempt myself. I'm looking to hear a couple of views on the actual installation though so I can at least understand what would be required.
I think before you worry about the 'actual installation' you need to check out the practicality and cost of upgrading your supply. If you can upgrade it to 70kW there will be a very different design approach to trying to manage with a 100A single phase supply.
 
Last edited:
Thanks, I understand that I'll need a professional for the installation and this isn't something I would attempt myself. I'm looking to hear a couple of views on the actual installation though so I can at least understand what would be required.
The biggest factor, as mentioned above, is the decision on upgrading the supply capability versus trying to manage your overall demand by other means (manual or automatic).

If you can afford to get more power available, then it becomes reasonably easy to look at the design of the outside supply sub-main once you know the supply characteristics (Zs, any need for TN-C-S sized extraneous bond) and the max load. You have several factors on that alone:
  • Current carrying capacity
  • Voltage drop
  • End of cable Zs for fault disconnection
Generally speaking it is better to put in a larger cable if you can afford it as it allows any future additions and also marginally reduces wasted power (though pay-back time can be quite long), but you have to start with what is the minimum requirement to meet all of the above.
 
However, if it is too expensive to upgrade then you are looking at means to limit the worst-case load. That could be various "shower priority" style units, or it could be something significantly more complicated.

EV chargers often allow for max supply management, it would be essential here to have that aspect, and desirable in any other case as well.
 

Reply to How to add ~25kw to garden? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
596
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
744

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock