How to add a bigger Back Box

Discuss How to add a bigger Back Box in the UK Electrical Forum area at ElectriciansForums.net

L

Lordy9099

Hello All,

Happy New Year! Anyway I have just bought a 2 way LightwaveRF dimmer switch, it is suppost to be used with a 35mm back box but the one installed is currently only 16mm and no way can I get it to fit, so my main question is how can I make the current 16mm hole into a 35mm hole without making a big mess. Also how do you make a cable bigger if it is getting a little too short, Choc block?

Thanks
 
To the OP -

it's not a hard job to do, but it does take a bit of practice to 'not make a big mess' as you say. Firstly, you need to tell us what the type of wall is - block/brick or stud partition? I'm guessing brick/block for now. Second, you need to measure the thickness ('leaf') of the wall and check that it's deep enough to accept a bigger box to start with.

Then, and only then.... turn off the power, remove the old fitting and box, use a 6mm ish size drill to stitch drill around the existing hole, have one big hammer and chisel session to remove the rest of it.

But before you do any of that, you'll want to check that you have a neutral at the existing switch if the dimmer needs one.
 
I tested the dimmer yesterday and it worked fine with the existing cables. How do you check the 'leaf'?

- - - Updated - - -

To the OP -

it's not a hard job to do, but it does take a bit of practice to 'not make a big mess' as you say. Firstly, you need to tell us what the type of wall is - block/brick or stud partition? I'm guessing brick/block for now. Second, you need to measure the thickness ('leaf') of the wall and check that it's deep enough to accept a bigger box to start with.

Then, and only then.... turn off the power, remove the old fitting and box, use a 6mm ish size drill to stitch drill around the existing hole, have one big hammer and chisel session to remove the rest of it.

But before you do any of that, you'll want to check that you have a neutral at the existing switch if the dimmer needs one.

I tested the dimmer yesterday and it worked fine with the existing cables. How do you check the 'leaf'?
 
buy yourself a fein multi master £ 150, tightly cut round the box, chisel through into the next room, bang in a 35mm box using plasterboard adhesive. total cost around £200. or pay a spark £50 to do the job. no brainer.
 
You can get collars from B&Q and the like, that go between the back box and the accessory.
These allow the extra space required when the back box is too shallow.
If your cables are too short, yes use a terminal block to extend them.
 
Get a ELECTRICIAN to do it instead of somebody f&ckin competant. I HATE that word competant and all its b&ll&cks definitions.

competent [ˈkɒmpɪtənt]adj
1.
having sufficient skill, knowledge, etc.; capable
2. suitable or sufficient for the purpose a competent answer
3. (Law) Law (of a witness) having legal capacity; qualified to testify, etc.
4. (postpositive; foll by to) belonging as a right; appropriate[from Latin competēns, from competere to be competent; see compete]

:laugh:
 

Reply to How to add a bigger Back Box in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock