Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss How to connect SWA armour to 6mm Twin and Earth cable in the Electrical Forum area at ElectrciansForums.co.uk.

Tags:
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. alban moffitt
    Offline

    alban moffitt EF Member

    Location:
    Border of Outer Hebrides
    Business Name:
    McKelectrictoshentire Ltd.
    I have run 6mm t and e through the house from the db in the garage on a 32 amp mcb which is rcd protected. the 6 mm cable then goes into the back of an ip66 rated JB on the side of the house. i then intend to run 2 core (live and neutral) 6mm swa up to a workshop using the armour as earth.
    my question is do i need to link the armour to the earth in the 6mm cable coming from the db in the garage and if so how do i do this.

    On the other end, in the cu in the workshop i have got a 20 a mcb for sockets and 6 a for lights. how do i connect the earth block in the cu to the armour from the swa?
     
    • Dislike Dislike x 1
  2. DPG
    Offline

    DPG Respected Member

    Location:
    S Yorkshire
    Based on your questions you need an electrician to do this work and also test it afterwards.
     
    • Agree Agree x 5
    • Winner Winner x 2
    • Like Like x 1
    • Optimistic Optimistic x 1
  3. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    I would strongly recommend you get an electrician in to complete your works.

    No disrespect, but your questions are basic ones however vitally important for the safety of your installation. Failure to have a broad spectrum of knowledge on the safety aspects of your electrical installation can lead to a simple but fatal error, unbeknown to you once installed.
     
    • Like Like x 2
    • Agree Agree x 1
    • Optimistic Optimistic x 1
  4. Spoon
    Offline

    Spoon Forum Mentor

    Location:
    Lancashire
    This work falls under Part P and is notifiable.
     
    • Optimistic Optimistic x 1
  5. Matthewd29
    Offline

    Matthewd29 Regular EF Member

    Location:
    Belfast
    If this armour isn't correctly glanced your going to end up with a dangerous situation with no earth. If you are unsure how to do this simply do not do it
     
    • Agree Agree x 2
    • Optimistic Optimistic x 1
  6. Cid
    Offline

    Cid Active EF Member

    Location:
    London
    You need swa cable glands. They come with the necessary earthing tag to connect the earth cable. Plenty of tutorials on YouTube on how to terminate swa cables correctly.
     
    • Like Like x 1
  7. alban moffitt
    Offline

    alban moffitt EF Member

    Location:
    Border of Outer Hebrides
    Business Name:
    McKelectrictoshentire Ltd.
    Thanks Cid,
    i will use a pirhana nut to connect the armour to the earth
    thanks everyone for their input
     
  8. SJD
    Offline

    SJD Forum Mentor

    Location:
    Braccan heal
    Why do some people use 2-core SWA in small sizes and small runs, when 3-core wouldn't cost much more?
     
    • Agree Agree x 8
    • Like Like x 1
    • Winner Winner x 1
  9. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    any extraneous metal pipes etc. in workshop?????
     
  10. alban moffitt
    Offline

    alban moffitt EF Member

    Location:
    Border of Outer Hebrides
    Business Name:
    McKelectrictoshentire Ltd.
    yes i can get hold of some easily
     
    • Optimistic Optimistic x 1
  11. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    my post concerned extraneous metalwork, if it's TNC-S system, the you need a 10mm bonding cable back to MET, ot TT the workshop.
     
  12. Barnaby Stedman
    Offline

    Barnaby Stedman EF Member

    Location:
    England
    Business Name:
    ServicesUK
    Id say get a pro like me on the job. i can come and quote today if you would like
     
    • Dislike Dislike x 1
  13. Andy78
    Online

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    Will you also be acting on the input to fully test and notify this circuit to building control ? Or are you just choosing to ignore the legal and safety aspects of this job in favour of the input that gets it done to your requirements ?
     
    • Like Like x 1
  14. alban moffitt
    Offline

    alban moffitt EF Member

    Location:
    Border of Outer Hebrides
    Business Name:
    McKelectrictoshentire Ltd.
     
  15. alban moffitt
    Offline

    alban moffitt EF Member

    Location:
    Border of Outer Hebrides
    Business Name:
    McKelectrictoshentire Ltd.
    i appreciate your concern andy78,
    of course it will be signed of and notified so rest assured all in good hands. my brother in law is a fully qualified electrician so he is more than capable of doing this
    and i work under him ;)
     
Loading...
Similar Threads - connect armour Twin Forum Date
Connecting light outside (1-way) to 2-gang (with a 2-way) Electrical Forum Sunday at 5:38 PM
Ax disconnection times 32A+ Electrical Course Trainees Only Jan 17, 2019

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job