Discuss How to properly do an RCD time trip test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

swaRRR

Esteemed
Reaction score
266
I've seen several videos on these, half of them show an MCB in the 'on' position protected by an RCD also in the 'on' position, earth lead on the earth bar, neutral on the neutral bar, and live on the MCB's line screw terminal.

But then i've seen other videos where the earth bar and the line/neutral terminals on the load/outgoing side of the RCD is used. John Ward for example shows this test with a standalone RCD on a rig board with two pieces of wire coming from line and neutral.

Which one is right?
 
Which one is right?

Both are right, as long as the live lead is connected to the outgoing side of the RCD the test will work.

If you're testing standard SP RCBO's then the neutral is solid anyway and it won't matter which side of it the neutral is connected.

And if you have an RCD which is downstream of another RCD you can connect the earth lead of the tester to the incoming N to avoid tripping the upstream RCD.
 
So when they leave a circuit on and test that it's technically not allowed?
In some circumstances it can be useful to see if an RCD is actually working in normal operating conditions too, e.g. that it isn't being blinded by DC leakage. A ramp test can be very helpful under load to see how close it is to tripping "normally"
No point signing off an RCD that works perfectly until you connect any loads!
 
Last edited:
In some circumstances it can be useful to see if an RCD is actually working in normal operating conditions too, e.g. that it isn't being blinded by DC leakage. A ramp test can be very helpful under load to see how close it is to tripping "normally"
No point signing off an RCD that works perfectly until you connect any loads!
Thanks for the help mate appreciate it. So i'm right in thinking that for test sheet purposes on an RCD time test we should try to test without a load, for the certs results box?
 

Reply to How to properly do an RCD time trip test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
388
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
610
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
622
Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...
Replies
6
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
936

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock