Discuss How to test RCD for lighting circuit in the DIY Electrical Advice area at ElectriciansForums.net

David427

DIY
Reaction score
0
I live in Australia; you can use a socket tester to test the RCD for the power outlet circuit. Plug device to a 3-pin wall socket, set testing mA to 30 on the device and press test button.

What is the best way to test RCD on the lighting circuit – from an existing B22 or E27 lamp holder? (Not from the meter box end).

(I have seen B22 to 3Pin female converters, was not sure if that would work.)

Thanks …
 
The problem that you have is a lack of earth at the actual lamp point - either design is just Neutral and Active by that point which means you can't actually 'leak' earth from a device. You also don't (normally) have a Neutral at the switches either, just the switched Active so that also doesn't work.

Therefore, if your mission is just to know if the RCD in the board works, you'll need a proper RCD tester to fit onto the RCD device at the board. Because, also if you were to overcome the issues above, found a means of testing and it failed to trip you'd still be none the wiser if it was a faulty RCD or a fault in the circuit wiring that you had an incomplete Earth or Neutral fault somewhere.
 
The problem that you have is a lack of earth at the actual lamp point - either design is just Neutral and Active by that point which means you can't actually 'leak' earth from a device. You also don't (normally) have a Neutral at the switches either, just the switched Active so that also doesn't work.

Therefore, if your mission is just to know if the RCD in the board works, you'll need a proper RCD tester to fit onto the RCD device at the board. Because, also if you were to overcome the issues above, found a means of testing and it failed to trip you'd still be none the wiser if it was a faulty RCD or a fault in the circuit wiring that you had an incomplete Earth or Neutral fault somewhere.

The problem that you have is a lack of earth at the actual lamp point - either design is just Neutral and Active by that point which means you can't actually 'leak' earth from a device. You also don't (normally) have a Neutral at the switches either, just the switched Active so that also doesn't work.

Therefore, if your mission is just to know if the RCD in the board works, you'll need a proper RCD tester to fit onto the RCD device at the board. Because, also if you were to overcome the issues above, found a means of testing and it failed to trip you'd still be none the wiser if it was a faulty RCD or a fault in the circuit wiring that you had an incomplete Earth or Neutral fault somewhere.
Appreciate the explanation, seems like a task for an electrician then?
Socket tester does basic wiring checks and indicates if all 3 wires are connected properly. Then I did the RCD test on one socket, to make sure RCD trips/works.
Is it necessary to do the RCD checks on all the power sockets or just one is enough?
 

Reply to How to test RCD for lighting circuit in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I'm moving a socket installed on a lighting circuit (installed by previous owner who was a professional electrician so I assume he knew what he...
Replies
7
Views
1K
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
669
Hi I have a Corby 7700 trouser press it is a 220w model, 3 years 10 month old. On Friday it stopped working, so I took it to the garage ready...
Replies
1
Views
708
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock