I asked at college recently if when working out Ib (design current) do we use the nominal voltage (which will be a constant of 230v in most instances) or do we use the MI chosen voltage. As an example I've seen appliances rated at 3kW/240v according to the packaging. So is the design current 3000/240=12.5A or is it 3000/230=13A?

The answer the lecturer gave was you always work out Ib at the nominal voltage, ignoring what the manufacturer instructions said. I was a bit suspect of this answer, so Gods.....

EDIT: Bit more info as to why I'm asking. It might not make much difference in most cases, but take the example of a 9.5kW shower. If you work out Ib at 240v you can safely select In as a 40A breaker. However, work out Ib at 230v and you have 41.3A, which would require a 50A breaker and in turn would likely affect the size of the cable you have to install too.

The KW would be lower at 230 than 240.
 
I asked at college recently if when working out Ib (design current) do we use the nominal voltage (which will be a constant of 230v in most instances) or do we use the MI chosen voltage. As an example I've seen appliances rated at 3kW/240v according to the packaging. So is the design current 3000/240=12.5A or is it 3000/230=13A?

The answer the lecturer gave was you always work out Ib at the nominal voltage, ignoring what the manufacturer instructions said. I was a bit suspect of this answer, so Gods.....

EDIT: Bit more info as to why I'm asking. It might not make much difference in most cases, but take the example of a 9.5kW shower. If you work out Ib at 240v you can safely select In as a 40A breaker. However, work out Ib at 230v and you have 41.3A, which would require a 50A breaker and in turn would likely affect the size of the cable you have to install too.

If you want to work out current drawn at different voltages then.....

As the resistance of the element is the constant you would work out that and then apply it to the voltage. Using your example of 3kW at 240V (sorry about the clumsy sum but I don't know how to type a squared symbol)

R=V*V/P
240*240/3000
R=19.2

P=V*V/R
230*230/19.2
P=2755

So 3000W at 240V is equivalent to 2755W at 230V. You can then work out the current drawn at each voltage.

In practice you would use the manufacturers higher rating as Ib.
 
If you want to work out current drawn at different voltages then.....

As the resistance of the element is the constant you would work out that and then apply it to the voltage. Using your example of 3kW at 240V (sorry about the clumsy sum but I don't know how to type a squared symbol)

R=V*V/P
240*240/3000
R=19.2

P=V*V/R
230*230/19.2
P=2755

So 3000W at 240V is equivalent to 2755W at 230V. You can then work out the current drawn at each voltage.

In practice you would use the manufacturers higher rating as Ib.

That's the answer I was looking for.
 

Reply to How to work out min cross sectional area of live conductors? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have pasted the question in below, I have no Idea how to do this of someone could give me the pages and a step by step guide would be perfect...
Replies
5
Views
4K
Afternoon all, How do i solve these two questions, Feel like am missing something simple. doing my head in lol. I need to learn the calculation...
Replies
24
Views
4K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
I suspect I know the answer to this already, but... For some reason, recently I've been getting increasingly ****** off by being undercut by...
Replies
11
Views
3K
Good evening all, was told that the trainee area would be a good area for me to go in and I've messaged Admin a couple of days back but haven't...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock