Discuss I Can't See How This Works... in the UK Electrical Forum area at ElectriciansForums.net

R

R1CH-G

Here's the scenario:

Ring Final Circuit

Design Current = 20 Amps
Circuit Breaker = 32 Amps (may well be using an RCBO - but that's another story)
Ring length total (end to end) < 45 meters
Correction Factors - grouping factor of 0.78 (reference method E with 9 other circuits)

Gives an Iz of just over 41 Amps

Where am I going wrong here, as I think wiring the ring in 10 mil T&E is going to be a little difficult!
 
Assuming I've understood the question, you've applied all your correction factors and need a cable with a 'raw' clipped-direct capacity of > 41A? OSG p.144 says 6mm clipped direct has 47A clipped-direct capacity. But also that would be for a radial not a ring, wouldn't it? Whole point of the ring is you can get away with smaller cable. Can't remember how you work it out for a ring. Would be interested to see the working from someone who can.
 
In essence a ring final circuit must have a corrected current carrying capacity of 20A for the conductors.
BS7671 states that this is the minimum CCC for ring final circuit conductors and the OSG states that at a ring is designed with a 20A load at the mid point and then 12A (to make up 32A) distributed evenly around the ring => equivalent to 26A at the mid point of the ring. and Appendix H OSG gives the guidance that the minimum CCC is 20A for a 32A ring final circuit.

In your scenario the ring length is <45m and the guidance in BS7671 says a 32A ring can be 100m2 and the OSG states that the maximum length can be up to 106m, so you would have a compliant circuit for length.

You need to apply the 0.78 grouping factor (and assuming there are no other factors) then you have 20A/0.78 = 25.64A
Therefore you are looking at a single phase multicore PVC covered cable installed to reference method E that can carry at least 25.64 A, from table 4D4A this would be a 2.5mm² cable (31A CCC).
 
Kerchof's law seems to ring a bell in my foggy brain

the sum of the currents entering as junction is equal to the sum of the currents leaving the junction. dunno what that's got to do with the OP.
 

Reply to I Can't See How This Works... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there I am struggling with the following calculation. 4mm Ring Final Circuit, In = 32A Cg - group of 6 with a correction factor of 0.57 Ci -...
Replies
10
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
824
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock