Discuss i keep blowing cooker elements, is my wiring safe? in the UK Electrical Forum area at ElectriciansForums.net

What do you mean by blowing? are they going open circuit? Tripping RCD/circuit breaker etc. I've seen fan oven elements have a shorter life when the fan is running too slowly, such as high friction in the fan motor.
 
As Freddo says but this problem can also be caused by a broken thermostat for the oven.The oven stat never clicks off and the element keeps getting hotter and hotter until it blows itself.To check the stat,put the oven on at 50 degrees c and give it a minute.It should click off at 50 and then turn it up to 100 and it should click off when it reaches 100.If the stat doesn't seem to be clicking then its faulty.
Another side point is that if the oven element is the back one with a fan in the middle then make sure that a: the fan is spinning and b: the cover is put back over the whole back area or else this will blow the element as it needs the air to be circulating around with the fan and the cover in place.
 
It is very unlikely that a fault in your wiring could damage the elements. If you have a normal single-phase consumer unit and meter, and none of your other electrical appliances or lights are behaving strangely, then any underlying connection between the element failures is probably within the oven as stated above.
 
It is very unlikely that a fault in your wiring could damage the elements. If you have a normal single-phase consumer unit and meter, and none of your other electrical appliances or lights are behaving strangely, then any underlying connection between the element failures is probably within the oven as stated above.
this is now the second oven in 3 years that has had the same issue. I have noticed that the cooker hood and an extra double socket are all wired into the cooker switch. could this be where the problem lies
 
this element lasted just over a year, I think the problem maybe the cooker switch socket as it also has the oven hood and a double socket wired into the back of it
Well that doesn't sound right for a starter. Possibly not the issue, but certainly not right?
 
I've checked the technical info on the oven and it says its 40A, the main fuse Is a 30A is this an issue
not really as the oven will not draw anywhere near 40A due to diversity ( that's because you won't hav all elements on at the same time and the stat/s cut them out. a 30A fuse will withstand 40A for somewhere around an hour.
 

Reply to i keep blowing cooker elements, is my wiring safe? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an electric oven - now many years old. I have replaced the main circular 2.5kW oven element (ELEHY6708) several times over the years...
Replies
9
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
736
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
I have measured the following readings to earth on a twin oven---- Element 1... 0.149, Element 2... 0.9, Element 3... 0.88 , Element 4 0.08...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock