Discuss I know DNOs are not obliged to provide an earth, but... in the UK Electrical Forum area at ElectriciansForums.net

happysteve

-
Esteemed
Arms
Supporter
Reaction score
2,115
I know DNOs are not obliged to provide an earth, but the actions of WPD today really surprised me.

Was asked to swap a socket-outlet, did the usual basic checks, no earth to the property. Suburban, underground supply, possibly former TN-S (vague suggestion of the stub of a clamp round the sheath, but had been painted over decades ago), more likely earth had previously been supplied by water pipe as no seperate earthing conductor evident. Ze (yes, I know it's not a proper Ze as it's through the bonding) 1.48Ω.

BS 3036 fuses, no RCD.

Called WPD, put it through as an urgent call as single fault = somebody possibly dies. Connected an earthing conductor to MET, left it dangling with enough slack for them to connect it to the Henley Series 5 neutral block.

Engineer attended (I wasn't there), would not connect earth ("upgrade" to PME) unless they paid £148. Happy to leave the installation in the state it was while they mulled it over. Their logic was, "it's been like that more than 30 years..." I have strongly advised the customer to get the work done, but they're 87 and it's a lot of money for them so they're going to think about it...
 
how easily could you whack a rod in and make it TT? its likely not going to be any worse than it is at present.
The whole dno not providing an earth thing needs changing, I have had success previously arguing for a customer when the earth on a tns was missing... they refused to connect one. I argued that they are obliged to as if there earth fails they can not legally leave the house powered up without an earth as in the time between them leaving and me putting a rod in, should somebody get a nasty shock and dies then its wpd who gets the blame.. not me.
If they provide an earth then they have a duty of care to maintain it and if aware of a fault or issue, then they are not allowed to just say no earth put a rod in, as they are liable even if they dont like to admit it.. all depends who you speak to.. i would ring back and tell them this.. ask to speak to the duty manager/engineer and if necessary the complaints team.
 
The issue here is that I'm not 100% certain they (WPD) ever did provide an earth. I said there was vague suggestion of a stub of a clamp around the PILC cable, but it might not have been. If they never did provide an earth to the property, I can see their argument for claiming they don't need to maintain it. And they're the only people who would know (unless my customer has some old black and white photographs of their service head with an earth strap on it, stored in a tin box somewhere).

It was their attitude of, "It's been fine for 30 years, we're not bothered," that shocked me. The only reason it's been fine for 30 years, is because there hasn't been a fault in that time. That's not evidence that things are ok to leave as they are, that's evidence that the customer's been bloody lucky!
 
Dipsticks!
Where is the property? Is it a one off or are there any others similar in the vicinity? If so, see if you can check their earthing state. If there is evidence of previous tns, as you say, it's up to them to renew or upgrade.
Push them on it.
 
very clever those chimpanzees .they can make anything over there beyond the great wall ,they can even send a man in to space .and boy how do they get them back if the guarantee runs out. :rolleyes:
 
We sometimes do charity work in rural areas installing boreholes and wellpoints in places where the women have to walk half a day for potable water. The only power available in the village was in a small communal hall (more like a shed the size of a double garage) which served as their meeting place, school, hospital etc. It had a 2-wire supply on a straight concentric cable and going by the volt dip under a known load the supply cable must have been at least 3 km long.

There was a small CU with no earth and a single socket circuit and a light circuit installed. At every socket and light point there was a link between the neutral and the earth screws which made it a TN-C installation to all intents and purposes. They said they'd never used the electricity since it had been installed several years previously by an Italian charity organisation because it gave them shocks which was hardly surprising given the length of the supply cable and lack of actual earth.

I ended up welding a large nut and fitting a lug to the borehole steel sleeve that went 140 meters into the ground behind the hall. I ran an earth to the CU from there and converted the installation leaving it sub-ohm TT.
 
We sometimes do charity work in rural areas installing boreholes and wellpoints in places where the women have to walk half a day for potable water. The only power available in the village was in a small communal hall (more like a shed the size of a double garage) which served as their meeting place, school, hospital etc. It had a 2-wire supply on a straight concentric cable and going by the volt dip under a known load the supply cable must have been at least 3 km long.
.
Where abouts in Yorkshire are you, Marvo?:D
 

Reply to I know DNOs are not obliged to provide an earth, but... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
If there isn't a 2-pole isolator there already, I usually get the client to arrange to get one fitted before I do a board change, either through...
Replies
20
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
830
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock