Discuss Identifying the system in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
9
Hi all, I'm trying to identify a supply. Visually the supply looks like a TNS. An earth clamp is around the metal sheath of the incoming supply cable to an earth terminal block. Three phases and neutral out of the Henley unit. When I was carrying out a loop test Line and Neutral at the distribution board, my Megger LT5 lights up as Line and Earth. Telling me it's a TNCS. My tester works properly as I tested it on a commercial DB the day before. Both line and neutral, line and earth.
The whole thing is suspect as I noticed a few errors and incorrect information throughout the main room.
Any help would be appreciated.

Thank you
 
A photo would be good so that we could come to the same conclusion. You may be getting the same readings due to another supply nearby as TNC-S.
 
Found the solution, it was on old LT5 instructions, a note on it says when loop testing Line and Neutral, the Line and Earth neon illuminates , not the expected Line and Neutral as you would have thought. I won't forget that one. Had to search the internet for that one.
I bought the loop tester last week. I used them 25 years ago. They are great for boards, lights, checking pipe work. I have a Robin multi tester and loop/PFC tester.
The system is a TNS.
I'm making sure I have the design criteria for and job I do, using The BBB.
 

Reply to Identifying the system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
Today I came across an earth cable from the earth bar in the DB that went directly into the incoming neutral side of the main switch. The DB is...
Replies
14
Views
2K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock