I have been out to a faulty immersion and have found that there is current through the thermostat. but no current after the next component between the two white wires. what is this and what does it do? and is it bypassable , repairable without having to change the whole element.

thanks
Mark
 

Attachments

  • immersion.png
    42.8 KB · Views: 93
It looks like a thermal overload stat (although it is not clear on the photo ^^^^as above it won't enlarge), if it is you should just push in the centre part to reset it. I would consider changing the t+e supplying it with HR flex aswell while you are on.
 
yep, it's a thermal cut out to stop the water boiling if the stat goes s/c. if the stat has a thermal cut-out, then you don't need this . bypass it if it's duff.
 
I dont think the stat has a resettable switch. i will go back and see if the tiny black object inbetween the two white cables is a button and see what happens.
I dunno why the pic was so small????? stoopid phone cam

Thanks guys
 
that little black button is the reset. if it clicks when you press it, then you should get continuity across the terminals. but be prepared to go back if it trips again.
 
that little black button is the reset. if it clicks when you press it, then you should get continuity across the terminals. but be prepared to go back if it trips again.


I was thinking exactly this, there is obviously a reason why it should trip in the first place, i may turn down the themostat a few degrees to see if it helps. I assume if it keeps tripping the thermostat isnt working properly.
 
I was thinking exactly this, there is obviously a reason why it should trip in the first place, i may turn down the themostat a few degrees to see if it helps. I assume if it keeps tripping the thermostat isnt working properly.

I think that I am right in saying that the stat should be set at above 50oC because of legionella, so bare that in mind.............
 

Reply to immersion fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hoping someone can give me some advice. My cyclinder immersion thermostat is tripping every few days. It hasn't been used for a few years, but...
Replies
6
Views
4K
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
471
Have just got back from a call out, where the clients' immersion had stopped working. The problem is the separate thermal safety cutout has...
Replies
12
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock