been to price up a job, customer just has just moved in, the requirement was a couple replacement of lights ,new security light.
I asked the customer that I need to see the c/u and check the main earth bonding.
looking at c/u the main bonding to the MET .wait for it was two 6mm earths
from the c/u to the MET . water & gas 10mm. flipped the lid down on the c/u and to see what the MCBs are on any RCDs not one.
the customer says the place was rewired in 2006 .any paper work for that ,at the solicitors the customer says .
I then told the customer you need to speak to your solicitor .
I was then told by the customer I have property's rented out and have c/u like that .like victor melldrew I don't believe it.
having spoken about the security light going out side the back door
the customer said I will get that of flebay only about £20 quid
you will fit it she said .I will fit it but their is no warrantee on you supplying me with that .customer saying warrantee from flebay .
f77king customers what do they know.
rant over
 
I’m confused, is the protective bonding in 10mm and the earthing conductor is 2x 6mm cables in parallel?
Plus is the MET not the earth bar inside the consumer unit?
 
Feel your pain Buzz. I went to house to look at moving 2 sockets as a recommendation. Straight forward job, so did a quick Zs on the existing sockets and got 14Ω :eek: Then after checking all the terminations on the sockets on the ring and did it again and got 1.9Ω.

Went to CU and opened it up :eek::eek::eek: what a mess!!! Did a Ze test and got 1.9Ω on the TN-S. The customer then piped up and said 'Oh we had a problem a couple of years ago with something in here. Our previous electrician did some work to some other sockets and then when he tested the board he was having problems. He made a phone call and some guys came out and messed around with something and said I didn't have to have my drive dug up and that it is all ok'. I asked if there was any paperwork relating to this previous work and they said no.

I'm now waiting for western power to sort it out. I expect to see a new electrode in place. Wasted an hour of my life for no reward.

Oh, the main earth was 16mm and the gas and water were 16mm also......
 
I’m confused, is the protective bonding in 10mm and the earthing conductor is 2x 6mm cables in parallel?
Plus is the MET not the earth bar inside the consumer unit?
I was always taught that the MET was the metal connector block outside of the consumer unit which has the DNOs incoming earth connected to it. Gas and water bonding is connected to this also and an earth cable is run into the consumer unit from this block. We dont place a Main Earth Terminal do not disconnect sticker inside a consumer unit.
 
Last edited:
I was always taught that the MET was the metal connector block outside of the consumer unit which has the DNOs incoming earth connected to it. We dont place a Main Earth Terminal do not disconnect sticker inside a consumer unit.
It can be either a standalone terminal or inside a DB, see the definition of an MET in 7671. A label is only required if the MET is separate from main switchgear
 
Last edited by a moderator:
I would say that the block externally is the DNO source of earthing as is often the case with TNCS supplies,and that the MET is the earth bar inside the consumer unit in which your protective conductors and earthing conductor connect to.
Often larger commercial installations will have an external MET where everything connects to other than your circuit cpc’s.
If it was TN-S with an earth connection onto the sheath ,you wouldn’t connect your main protective conductors to the sheath of the incoming supply say Or mess about fitting an earth block.
Obviously if this is the case you don’t label it inside a consumer unit.
 
Last edited:
Ok i might be opening up a can of worms here lol but i have only come across a DNOs incoming earth connected into a metal earth block that is attached to the wooden board in all earthing arrangements on domestic premises TT excluded for the minute.
In both TNCS/PME and TN-S the DNOs earth is connected into the external MET block. I class external as not in the consumer unit and not enclosed so it is visible. Bonding cables are connected into the MET and i have never connected gas/water bonding cables inside a consumer unit. Even in my books it is called main earth terminal and is the connection point for all our other earth connections.
 
it depends on how you bond to the water services& gas .
some times you could use the earth terminals in the c/u
or use the metal earth terminal on the board to the gas /water services by looking on pages 17&18pages on the osg .
 
Ok i might be opening up a can of worms here lol but i have only come across a DNOs incoming earth connected into a metal earth block that is attached to the wooden board in all earthing arrangements on domestic premises TT excluded for the minute.
In both TNCS/PME and TN-S the DNOs earth is connected into the external MET block. I class external as not in the consumer unit and not enclosed so it is visible. Bonding cables are connected into the MET and i have never connected gas/water bonding cables inside a consumer unit. Even in my books it is called main earth terminal and is the connection point for all our other earth connections.
My example would be take a new build installation TN-CS.
Meter and cut out is in an external meter box.
DB is internal 3 meters away say in the garage.
Where would you connect your main protective bonding conductors?
Bear in mind there’s no external earth block fixed to a wooden board the source of earthing is part of the cut out and the terminals are accessible with a hex key only.
 

Reply to inadiqate bonding from the consumer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
680
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
Hi I know I have to do more testing but I just want to see if there is something I’m missing. Customer said light fitting in the loft was...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock