hi everyone
3 phase mains coming into building split 1 phase for each of thee 3 flats. now 2 flats are converted into one and rewired my question is do i still use 2 phases for 2 fuse board to balance the load or do i use 1 phase and leave another one unused
any thoughts well appreciated
 
To be honest though not ideal I would rather have a spare phase on the system than having 400 volts in a domestic situation.

As it is now 2 flats, from 3 could you use that 3rd phase for communal areas, though it won't have the same load, it will still have some load on it.

Also it will enable you to use the one CU for the property rather than using the 2 just to use 2 phases.
 
Last edited:
You have the option of using only one phase (per flat leaving the third redundant) or you can have the DNO come out to change the service to a two phase supply. Mainly you need to make sure the neutral conductor size will suffice if you're to settle for the first option as I don't think it's going to be easy balancing 3 phase with 2 flats. Cheers
 
good advice sparks about the neutral size but I would imagine in a domestic situation it will be the same size as the LINE, but your right you need to make sure as it will be unbalanced, it can carry that load.

Once you start calling the DNO you can actually hear the pound signs rattle up over the phone lol, so I would try and utilise the 3rd phase for communal
 

Reply to incoming 3 phase in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
572
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
947
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
647
My daughter lives in a flat in London in converted circa 1900 5 storey terrace in Bethnal Green. She is considering getting a Stiebel Eltron...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock