Morning All!
Firstly sorry if this is in the wrong section, it wouldn't let me post in the DIY bit where i thought this should have gone.
I've got a problem with my extractor fan staying on (new installation)
It's a 'manrose' inline extractor fan with a timer.
i've searched countless amounts of times around several forums but cant find a solution so i'm resorting to asking for help
I'm powering the fan from the lighting loom, live to live, neutral to neutral, switched live to switched live.
BUT when i test the circuit when the lights are OFF there is still a phantom/ghost/induced voltage of about 50v still showing and i'm assuming that, is what's keeping the fan in the ON position.
I'm using a digital voltmeter so i'm aware this can be too sensitive etc etc but something is still keeping the fan on.....
Any ideas?
I'm so lost and frustrated at this not working!!
Firstly sorry if this is in the wrong section, it wouldn't let me post in the DIY bit where i thought this should have gone.
I've got a problem with my extractor fan staying on (new installation)
It's a 'manrose' inline extractor fan with a timer.
i've searched countless amounts of times around several forums but cant find a solution so i'm resorting to asking for help
I'm powering the fan from the lighting loom, live to live, neutral to neutral, switched live to switched live.
BUT when i test the circuit when the lights are OFF there is still a phantom/ghost/induced voltage of about 50v still showing and i'm assuming that, is what's keeping the fan in the ON position.
I'm using a digital voltmeter so i'm aware this can be too sensitive etc etc but something is still keeping the fan on.....
Any ideas?
I'm so lost and frustrated at this not working!!