Discuss Induction hob and oven install in the UK Electrical Forum area at ElectriciansForums.net

Adams dad

DIY
Reaction score
1
Hi, replacing gas hob with Zannusi 7.3kw (max)32a induction hob, and oven with aeg 3.2kw(max) 16a. I was going to put hob on existing 32a 6mm separate circuit, simple swap. However, my question is, can I put the oven on the other 32a kitchen ring circuit? Both require hard wire not plug and play. Any advice gratefully received.
 
The existing 6mm circuit can supply both oven and hob, by fitting a dual outlet plate.
At 3.2kW the oven is on the limit to run off a 13 amp plug, and many manufacturers state that a 13 amp plug should not be fitted, so would you not be able to supply it from the ring final circuit.
 
The existing 6mm circuit can supply both oven and hob, by fitting a dual outlet plate.
At 3.2kW the oven is on the limit to run off a 13 amp plug, and many manufacturers state that a 13 amp plug should not be fitted, so would you not be able to supply it from the ring final circuit.
Hi, that's what I was thinking, but didn't want to overload the 32a kitchen ring. Wasn't sure as it has kettle, microwave etc?
 
agree.put oven and hob on the existing dedicated 32A circuit, using a diaul cooket outlet, no need to touch the ring.
 
So, put the induction hob at 7.3kw and the oven at 3.2kw on the original 32 amp 6mm oven circuit. Will that be ok? I wasn't too sure if I could do that. Thanks for the help ?
that's right. the current draw of cooking appliances never gets as high as the rating as :

1.not all elements are used together,and:
2. thermostats cycle elements on and off,
 
that's right. the current draw of cooking appliances never gets as high as the rating as :

1.not all elements are used together,and:
2. thermostats cycle elements on and off,
Completely confused now. Had an electrician out yesterday and has told me I'll need a separate circuit installing for the oven ?. For the love of god, what do I need to do ?
 
Completely confused now. Had an electrician out yesterday and has told me I'll need a separate circuit installing for the oven ?. For the love of god, what do I need to do ?
Make arrangements via an experience Electrician for a new circuit to allow for your new circuit
 
Thanks DefyG, so I'll be ok to run it off the existing 32a 6mm circuit to double outlet. Sorry to be a pain, but getting so many mixed messages ?
got it. both oven and hob togehther on a 6.0mm , 32A dedicated circuit. worked for 60 years so far.
 

Reply to Induction hob and oven install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
950
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
809
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
692
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K
Hi all, I'm getting a 32a induction hob and a 13a oven installed as part of a kitchen refurb. The existing cooker circuit is 6mm protected by a...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock