Discuss Industrial Radials in SWA in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hello all,

Trained years ago, not done much for about a decade but I've been asked by a friend to add 5x double sockets into an industrial unit, my thinking is to use a radial 32A RCB, 4mm 3-core SWA cleated to the wall (moderate impact risk). Area is small, only about 2-3m from the distribution board and there is no need for any spurs etc. I don't have a bender etc any more so don't fancy metal conduit. Appliances are almost all (very) inductive so C-curve.

I did do 18th in 2020 but haven't got a book handy, sorry if this is an egg-sucking question but can't recall current regulations for running radials. Not something I've done for several years and I recall 'something' had changed. Used to be 20A/2.5/50m2 if I recall but I know thinking has changed(?).

Cheers,
Ben
 
‘very’ inductive items may need type D. Obviously you need low enough impedance to achieve disconnections times when choosing the type.

Calculate it before installing or wing it and test which I’m sure it will be the latter.

Getting 2 4mm SWAs into the back of a metal clad sounds like fun but the domestic boys manage with twin and skin.
 
32A radial of the sort of length in SWA clipped to wall, etc, is no problem but you ought to look up regs for actual rating, etc.

You will almost certainly need RCD protection so a RCBO would be needed, but you are unlikely to need it C-curve if for 13A sockets (unless more than one load switched at once) but check the manufacturer's information just in case.
 
and to add you don't even need a threader anymore for such a job I use ConLok on jobs like this and love the stuff. makes it so much quicker just fix the box , pop the conduit in and wind up the little grub screw. bosh
 
I think pretty much every sparks now uses 4mm for industrial / commercial radials , 4mm in / out in a double socket no problem if cut and dressed neatly
 
and to add you don't even need a threader anymore for such a job I use ConLok on jobs like this and love the stuff. makes it so much quicker just fix the box , pop the conduit in and wind up the little grub screw. bosh
Is it like the old slip tube DD, didnt think this was used in the UK anymore, the Americans use that kind of conduit system.
 
Interesting stuff, thanks all.

I have done 4mm SWAx2 in to sockets before, but as rightly pointed out it's a bit of a squeeze, that said the installation allows me to just put couplers between the boxes so I could actually just use singles between the boxes which would make life easier.

Found my book, and all looks fine in 4mm, although the price of Crabtree Polestar RCBOs is quite something! I'm sure they didn't used to be quite 'that' expensive! Fortunately, I'm not buying the parts!

Of course, a 'B' will be fine as it's highly unlikely the loads will be simultaneously switched as @pc1966 correctly reminded me! That's what happens when you've not done anything for 10+ years!

Thanks again all,
Ben
 

Reply to Industrial Radials in SWA in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
718
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hello all. I have just bought my first house but it needs a bit of work. I am re-wiring it and I've found the conservatory ring has been spurred...
Replies
11
Views
2K
I'm unsure if I should be an electrician or maybe another trade is better. I have basically completed my first year of a foundation in...
Replies
9
Views
698
Hi Folks , Just looking for a bit of advice as I'm looking to get back on the tools so please bare with me if this is a bit long winded. I'm a...
Replies
1
Views
601

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock