Discuss Inspection question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

mhar

-
Esteemed
Arms
Reaction score
414
527.2.1.
A flat with a multitude of downlights. I am not convinced that the G5.3 fittings are firerated and they are mounted through a double boarded ceiling which is a fire barrier (confirmed with the original architects). The fittings are made from a pressed metal which is very thin and are secured by sideways pressure springs into the hole with barely 1mm of the surround covering the ceiling hole - easily disturbed leaving a gap. There are no markings at all on the lights, not even a manufacturers name. On the plus side these fittings do not have any vent holes, there is some seal (I would guess IP3X) where the cables enter but this does not appear to me to be an intumescant material.
Whilst I passed my 2391 a year ago this is my first EICR as I have held back knowing that the inspection side would be my weakness and I required more experience, however I thought that a flat converted only 6 years ago and with only four circuits should be pretty straightforward!
As I am unable to verify if these are fire rated then the simple answer would be to put n/v against this section and to recommend further investigation however I am not comfortable with this as the other flats in the block are likely to be the same as they were converted at the same time and the building could be an accident waiting to happen if my suspicions are correct and my customer does not investigate further. Also he is likely to ask me to investigate further! Building control are not interested.
I have searched to see if a 2006 fire rated light should bear any symbols but it appears that it is sufficient for the symbol to be on the packaging, perhaps I am using the wrong search terms?
Advice please
 
A bit of a grey area this one. Its hard to picture what you are describing, but my first concern is that they sound to be too small for the hole that they are in, and as such the seal will not sit against the ceiling properly irrespective of fire rated or not.

Some fire rated down lighters don't always appear to be fire rated, when in fact they are, as they can be fire rated due to the fact that they will self extinguish if they catch fire.

A good clear couple of photos may help if you can upload some.

Cheers…………Howard
 

Reply to Inspection question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
874
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
792
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello, I am an enthusiast amateur undertaking wiring of two outbuilding under a building notice. I am soon to be subject to a first fix inspection...
Replies
5
Views
967
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock