Discuss inspection & test, disconection times & maximum zs allowed in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

V

vincef

Hi,

on a tn system, 238vs, would the disconnection time be 0.4s or 0.2s, i thought as over 230vs it should be 0.2s, but working with another engineer who disdagreed & pointed out tables in bs7671 show 0.4s to 5s?
Also when completing certs should you include the 80% or not in the maximum allowed zs box?
 
Hi,

You use the max Zs from the regs book for the cert and you only apply the 0.8 to these readings when your comparing your measured Zs results. However you dont need to use the 0.8 rule of thumb when comparing your measured results with the ones in the osg, as these have already been done for you.

Jay
 
disconnection time for circuits<32A is 0.4 secs . on a TN system. your 238V is classed as 230V nominal although it's really 240V.
 
don't get me going on yewrup. i''lll end up getting a ban, bloody foreign bureaucrats telling us what to do, we need another agincourt, trafalgar, waterloo, el alamein, grrrrrrrrrrrrrrrrrrrrrrrrrrrrrrrr
 
the foundations of Westminster Abbey are shaking. it's Winston turning in his grave.
 

Reply to inspection & test, disconection times & maximum zs allowed in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K
SORRY FOR LONG POST. So i have my 2391-52 multiple questions coming up on Friday 13th, ( yeh i know) and was giving some things to study over by...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock