Hi all and thanks for letting me join your forum. I am an old school electrician who has now retired.
So I need some advice, please. I have just moved into a new build house.
It has a 6mm swa cable that terminates in a waterproof box at the side of the house, which then feeds the garage. it s on its own 32A circuit with a type A RCD protecting it.
Is there any reason why I cannot run a second 6mm swa from the box on side of the house to a car charging point?
Seeing that the garage and the car being charged would never be used at the same time?
Look forward to your reply.
Thanks in advance.
MS2857
 
It’s far from ideal, a lot of people have freezers and tumble driers in the garage, not an inconsequential load as you are aware.
could you not install the charger from the garage distribution board?
many come with a current sensing clamp and could be configured to reduce its usage if other loads were on at the same time.
 
Hi all and thanks for letting me join your forum. I am an old school electrician who has now retired.
So I need some advice, please. I have just moved into a new build house.
It has a 6mm swa cable that terminates in a waterproof box at the side of the house, which then feeds the garage. it s on its own 32A circuit with a type A RCD protecting it.
Is there any reason why I cannot run a second 6mm swa from the box on side of the house to a car charging point?
Seeing that the garage and the car being charged would never be used at the same time?
Look forward to your reply.
Thanks in advance.
MS2857
Depends on what else you'd use this 32A supply in the garage for.
 
IF and thats quite an important If the swa feeding garage is 6mm SWA then the OCPD could potentially be uprated to give some room for ev charger and other appliances.
The zappi is the first option that comes to mind as you can fit multiple ct clamps. 1 for the main service fuse but also one for the garage consumer unit/feed so that the charger and other garage loads will not overload the garage supply. you treat the garage board as a 'group' in the settings. if combined loads in the garage reach the OCPD rating then the charger throttles down until safe to go back up to the max limit. since most people charge overnight its likely any other loads would be during the day so not be an issue anyway.
 

Reply to installing an EV CHARGING POINTS in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top