I'm currently renovating a my new home which is a late Victorian house, and I've plaster off a couple of stud walls in my office. With in the room, there are currently (The house was rewired around 7 years ago).
  • 1 Run of 1.5mm T + E for the lighting Circuit (running from floor to ceiling ~2.7m run)
  • 1. Run of 1.5mm for the light switch
  • 2 sockets with 2.5mm T + E at 45cm height
I'm wanting to add some sound insulation to these walls, but I understand this will derate the cable which is installed. What is the correct method to deal with it, it leaving some spacing around the wires (if so how much?) or using conduit the correct approach here?
 
The 1.5mm2 T&E for lighting / switch is likely to be very adequately rated even buried in insulation for a typical house.

The socket circuit may be a concern, depends what the wiring is (part of a ring with 2 cables to each socket, or a spur) and the circuit (32A ring final, or 16A / 20A radial). Simplest option is to just leave out some insulation around the cables, if that doesn't compromise the soundproofing.
 
The 1.5mm2 T&E for lighting / switch is likely to be very adequately rated even buried in insulation for a typical house.

The socket circuit may be a concern, depends what the wiring is (part of a ring with 2 cables to each socket, or a spur) and the circuit (32A ring final, or 16A / 20A radial). Simplest option is to just leave out some insulation around the cables, if that doesn't compromise the soundproofing.
As above. I would add that you may find it helpful to check what house circuit the sockets in question are on? It may very well be that if the circuit concerned is controlling bedroom sockets rather than kitchen sockets than in practice it will be lightly loaded. If your CU is, nt labelled just plug a radio in to the sockets in question and switch off mcbs one at a time until radio stops. Ditto the other sockets. Label your CU accordingly.
 
Hi - if I’ve understood correctly your Electrician needs to run the power circuit cable in accord with Method 102# from Table 4A2 of BS7671 for that part of the circuit. That should be possible with the wall opened.
 

Reply to Insulating a stud wall with existing cabling in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
1K
Hi All, Wondering if I can get some advice. Basically I’m having exposed joist ceilings in my house and I’m in the process of slowly changing all...
Replies
5
Views
1K
I'm installing smart modules in my light switches which means I need to replace the existing 25mm back boxes with 47mm ones. Downstairs all walls...
Replies
0
Views
324
Hi, I'm about to reroute cables and sockets/switches from the ceiling down to the socket height after insulating a wall. I understand this will...
Replies
2
Views
185
DIYer here. I'd like to install an electric car wall charger myself. It calls for 6/2 romex which I have. Unfortunately my panel is in my...
Replies
0
Views
663

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock