Search the forum,

Discuss Insulation Resistance Calculation in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Reaction score
13
Hi, I have an engineer who is completing his 2391-52 exam tonight and he has been told one of his mock questions was wrong, I have completed the working out myself and came up with the same answer as him, so either the paper is wrong or something has literally left my mind!!

"Determine the overall insulation resistance where the individual readings for four circuits are: 200M ohms, 100M ohms, 50M ohms & 20M ohms"

1/RT = 1/R1 +..... you get the picture.

1/200 = 0.005
1/100 = 0.01
1/50 = 0.02
1/20 = 0.05
Total = 0.085
1/0.085 = 11.76470588235294 (11.76 rounded)

The 4 multiple choice options are:
a) 1.68M ohms
b) 16.8M ohms
c) 16.8 ohms
d) 168 ohms

Please re-educate me and tell me where I am going wrong!
 
You are both correct, which answer did he go for?

Is this for the on-line exam aspect?

When carrying out work, I would use the calculation just as you have, but in the exam as it's multiple choice I would just use logic.

It can't be bigger than the smallest measurement (so nothing greater than 20M), and can't be anything lower than a factor of 2-3 lower (even if there were two 20M - in parallel these would be 10M so much less than that couldn't be the case), which usually narrows it down to only one answer.

The mock exam questions can often be complete nonsense!
 
Hi, I have an engineer who is completing his 2391-52 exam tonight and he has been told one of his mock questions was wrong, I have completed the working out myself and came up with the same answer as him, so either the paper is wrong or something has literally left my mind!!

"Determine the overall insulation resistance where the individual readings for four circuits are: 200M ohms, 100M ohms, 50M ohms & 20M ohms"

1/RT = 1/R1 +..... you get the picture.

1/200 = 0.005
1/100 = 0.01
1/50 = 0.02
1/20 = 0.05
Total = 0.085
1/0.085 = 11.76470588235294 (11.76 rounded)

The 4 multiple choice options are:
a) 1.68M ohms
b) 16.8M ohms
c) 16.8 ohms
d) 168 ohms

Please re-educate me and tell me where I am going wrong!
Just so everyone know's (I don't think this is breaking any rules) this is question 12 from Mock paper 2391-52 paper 2
 
I just checked on the C&G website, there is only one mock test for 2391-52, and question 12 is not this (anyone can access these)

Are you sure it's not a centre's version, or from spxxxxfaxxxts website, these are generally wrong, - questions from earlier editions which are no longer applicable to downright wrong!
 
I just checked on the C&G website, there is only one mock test for 2391-52, and question 12 is not this (anyone can access these)

Are you sure it's not a centre's version, or from spxxxxfaxxxts website, these are generally wrong, - questions from earlier editions which are no longer applicable to downright wrong!
totally agree. Been on that website and their mocks are full of errors. I did an 18th mock that had a 16th edition relevant question in it.
 
Hi, I have an engineer who is completing his 2391-52 exam tonight and he has been told one of his mock questions was wrong, I have completed the working out myself and came up with the same answer as him, so either the paper is wrong or something has literally left my mind!!

"Determine the overall insulation resistance where the individual readings for four circuits are: 200M ohms, 100M ohms, 50M ohms & 20M ohms"

1/RT = 1/R1 +..... you get the picture.

1/200 = 0.005
1/100 = 0.01
1/50 = 0.02
1/20 = 0.05
Total = 0.085
1/0.085 = 11.76470588235294 (11.76 rounded)

The 4 multiple choice options are:
a) 1.68M ohms
b) 16.8M ohms
c) 16.8 ohms
d) 168 ohms

Please re-educate me and tell me where I am going wrong!
 
Hi, I have an engineer who is completing his 2391-52 exam tonight and he has been told one of his mock questions was wrong, I have completed the working out myself and came up with the same answer as him, so either the paper is wrong or something has literally left my mind!!

"Determine the overall insulation resistance where the individual readings for four circuits are: 200M ohms, 100M ohms, 50M ohms & 20M ohms"

1/RT = 1/R1 +..... you get the picture.

1/200 = 0.005
1/100 = 0.01
1/50 = 0.02
1/20 = 0.05
Total = 0.085
1/0.085 = 11.76470588235294 (11.76 rounded)

The 4 multiple choice options are:
a) 1.68M ohms
b) 16.8M ohms
c) 16.8 ohms
d) 168 ohms

Please re-educate me and tell me where I am going wrong!
 
hi ben you said earlier you had someone completing his 2391-52 .
can please ask how he got on and did he discuss the course and how it was laid out.
i ask because i to will be doing this course of inspection and testing .
ben i would be so grateful if you had any information oh and yes i feel this question is wrong too
yours sparky jim
 
hi ben you said earlier you had someone completing his 2391-52 .
can please ask how he got on and did he discuss the course and how it was laid out.
i ask because i to will be doing this course of inspection and testing .
ben i would be so grateful if you had any information oh and yes i feel this question is wrong too
yours sparky jim
Hi Sparky Jim,

This thread was 4 years ago unfortunately, I would only muddying the waters if I were to offer the course lay out, I did mine in 2017 and the engineer in question on this thread no longer works for us.

Sorry about that, but I do wish you all the luck, hopefully you will smash it :)
 

Reply to Insulation Resistance Calculation in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock