Hi, I have an engineer who is completing his 2391-52 exam tonight and he has been told one of his mock questions was wrong, I have completed the working out myself and came up with the same answer as him, so either the paper is wrong or something has literally left my mind!!
"Determine the overall insulation resistance where the individual readings for four circuits are: 200M ohms, 100M ohms, 50M ohms & 20M ohms"
1/RT = 1/R1 +..... you get the picture.
1/200 = 0.005
1/100 = 0.01
1/50 = 0.02
1/20 = 0.05
Total = 0.085
1/0.085 = 11.76470588235294 (11.76 rounded)
The 4 multiple choice options are:
a) 1.68M ohms
b) 16.8M ohms
c) 16.8 ohms
d) 168 ohms
Please re-educate me and tell me where I am going wrong!