Discuss Insulation resistance problems in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

newfutile

-
Esteemed
Arms
Reaction score
388
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth.
When I disconnected the neutral from the neutral bar it's 116 MegOhms lowest (on the outside bollards).

However measuring from disconnected neutrals to earth all read over 200 MegOhms.

So it does not comply as measured but complies with neutral disconected.

Does anyone have an idea why? Screenshot_20230327_101216_Gallery.jpg
 
TL;DR
Interesting IR readings
What voltage were you using for the IR test? Maybe the neutral was being pulled down to earth via surge arrestors somewhere on another circuit.
 
If I understand you right, every circuit individually achieves over 200MΩ but when the neutrals are commoned, one circuit reads 1.4kΩ L-E? Do we know what the aggregate N-E reading was at that moment? You mention bollards; presumably this means permanently-connected lighting loads (on which we preferably wouldn't be testing L-E and N-E separately.) If there was any kind of N-E fault anywhere on any circuit, commoning the neutrals with it will equally affect the line on any circuit with load. I would be wondering what if anything was disturbed that created an intermittent low IR on the neutral bar, even if it only happened to manifest while testing the line.
 

Reply to Insulation resistance problems in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
198
I was checking the IR on a socket circuit and found 0.4M between neutral/earth. The reading came from a garage door motor that was plugged in...
Replies
8
Views
2K
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
414
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock