Might be trivial question. My understanding is that we test on either leg of the ring since both legs make up a radial, but some say they test both legs at once, i.e. LL to NN, it would make sense if the other leg is not insulated since this is a live test, but I don't see why not if the other leg is "wago-ed".
 
if you disconnect both L and N from DB, all you have then is 1 long radial.testing either end of L or N to E will give you your IR readings. you can test L-N as long as nothing is connected.
 
some say they test both legs at once, i.e. LL to NN, it would make sense if the other leg is not insulated since this is a live test.

It is not a live test, it is a dead test. The IR test is performed with the circuit isolated (dead).

As long as you have proved ring continuity before doing the IR test then it does not matter if you connect to one L or both etc
 
I know it's a test done on an deenergized board/circuit but you still send 500V through the circuit so it's kind of live.
IT'S a dead test Mate, voltage is applied not sent through
 
Sorry mate, I'm not a linguistics engineer, what's the principal difference between "sending" and "applying" in this context.
Volts don't flow. are not sent anywhere, they are a pressure that is applied to a circuit to put it in Layman's terms.
 
So you virtually can't get a shock from it?
What makes you think you wont get a belt from an insulation tester probably set at 500V dc, put it another way don't grab hold of the IR test leads when Applying the voltage.

Did you not cover Potential Difference and Current flow during your training?

Being a dead test means the the supply to the circuit is isolated, switched OFF, as you would in any dead test, never had the pleasure of some Sparky telling you to " hang on to these leads a second Mate please and pressing the test button, or in my Apprentice days winding the handle on an IR tester?

No I guess not. Makes yer eyes water a bit, and wakes you up, frowned upon these days though,
 
Last edited:

Reply to Insulation resistance test on a ring final circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
638
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
299
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Just done my exam, passed everything except Insulation Resistance... I can't think how I could've failed because it isn't the hardest thing on...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock