SPARTYKUS
moddeydhoo
as I said, not high enough for me, for a new circuit. Different when reporting on an existing install. It also says just below your quoted reg
"Insulation resistance values are usually much higher than those of Table 61"
Regulations are that, regulations. In effect a guide. The values in Table 61 are the minimum. If they are that low or lower than the infinite reading on your Megger / Fluke / Robin / whatever then ... there is a reason!
the other point I was trying to make to the OP was that it is better to find the fact for the low reading rather than just hoping it will be ok! Facts are good with electrical installations. Guessing is not
as I said, not high enough for me, for a new circuit. Different when reporting on an existing install. It also says just below your quoted reg
"Insulation resistance values are usually much higher than those of Table 61"
Regulations are that, regulations. In effect a guide. The values in Table 61 are the minimum. If they are that low or lower than the infinite reading on your Megger / Fluke / Robin / whatever then ... there is a reason!
the other point I was trying to make to the OP was that it is better to find the fact for the low reading rather than just hoping it will be ok! Facts are good with electrical installations. Guessing is not