moddeydhoo

as I said, not high enough for me, for a new circuit. Different when reporting on an existing install. It also says just below your quoted reg

"Insulation resistance values are usually much higher than those of Table 61"


Regulations are that, regulations. In effect a guide. The values in Table 61 are the minimum. If they are that low or lower than the infinite reading on your Megger / Fluke / Robin / whatever then ... there is a reason!

the other point I was trying to make to the OP was that it is better to find the fact for the low reading rather than just hoping it will be ok! Facts are good with electrical installations. Guessing is not
 
Last edited by a moderator:
I have been testing for years and years, 1 meg ohm, i would take a look for damp or damage on a circuit, simple to brerak down, and test, over 2 would not waste my time, stick it to 10o0v and test 99 times out of 100 the ohms will rise, damp.
 
I've always worked on the principle that it's better to track down the cause of unexpected readings. Even if the only thing it does is satisfy my curiosity and improve my knowledge.

If it turned out to be a crushed/damaged cable better to deal with it now than later.

Joiners have a terrible habit of trapping cables when putting up plasterboard etc.
 
50 million ohms is a huge number but another way of looking at it is less than 10% of the expected result.
 
On any NEW installation that is having it's first or initial recorded circuit IR tests, then you should always be testing for at least a 1 minute duration. Those lower than expected values will almost certainly be due to the surrounding damp conditions. Another very good reason to take 1 minute IR readings rather than the usual few seconds....
 
i've come accross this too, and after much consideration I just put it down on the cert. last month i done one and all circuits were around 100M and rising L+N - E but it was just plastered that day so what can you expect.
 
2m on a new build and your happy... Mmm ok bud me thinks not. I appreciate its a pass in the regs but in my opinion there's is a reason in which why its low and with that reading would spend a little time investigating the fault.
 
I have been testing for years and years, 1 meg ohm, i would take a look for damp or damage on a circuit, simple to brerak down, and test, over 2 would not waste my time, stick it to 10o0v and test 99 times out of 100 the ohms will rise, damp.

Why test at 1000v?
 

Reply to Insulation resistance test on new circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
614
Hello, I’ve got my AM2S coming up and I’ve been revising like mad but I’m stuck on something. I’ve read that it’s a 3 phase board with just...
Replies
11
Views
3K
I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch...
Replies
9
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
647

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock