Discuss Insulation Resistance test question? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Thanks for response guys. The main reason for the question was I got into an debate with someone at work as I was doing an IR test and the meter was climbing slowly but climbing never the less. He said there is a fault on the newly installed circuit where a cable may have been nicked/burned when pulling them in ( was effortless to run no chance of burning). I said to him more than likely the environment we are in is a little damp & cold and the plastering has recently been done so residue moisture in the air and at terminations may be making the meter climb slowly. Which I still believe to be the case. Also there are no loads as we are at the beginning of second fix of accessories for a load reading to be causing test effect. The meter is in good order and I have retested a length of cable with perfect results. We powered up the circuit and it held fine with rcbo in place. but he believes there is a fault.


Thanks again for feedback guys!!
 
Agree with your thoughts OP, often see it when IR testing in old or cold properties, the readings progressively rise the longer you leave the probes connected as it warms the cable a bit. within 30 secs it can go up a few hundred Mohms. So unless you have a clear short i wouldnt worry too much,
 
Agree with your thoughts OP, often see it when IR testing in old or cold properties, the readings progressively rise the longer you leave the probes connected as it warms the cable a bit. within 30 secs it can go up a few hundred Mohms. So unless you have a clear short i wouldnt worry too much,

Warms the cable? Tesla batteries in that MFT? :)
 

Reply to Insulation Resistance test question? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
568
Hi. The question is..... can saturated ground affect earth resistivity testing equipment? Some days there's an unacceptable earth reading, another...
Replies
8
Views
346
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
654
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
805
Hi all, if I’m getting an insulation reading of 0.03 across N & L on a lighting circuit what would cause this? Neutral earth, live earth, are in...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock