Easy, main switch off, all MCB's closed or fuses in place, lead with croc clip on both ends from neutral bar to busbar, or if this cannot be done, a nice bit of single between the neutral bar and the outgoing side of any MCB, seeing as they're all connected through the busbar it matters not which one.
This is entirely acceptable for periodics, with limitations noted. You can't always know what sensitive equipment may be hiding here and there, i.e. alarm spurs, TV boosters, so I always go down this route myself.
A new installation should have been tested way before all the final circuits were terminated anyway, so you wouldn't have to think about RCD's in line...