Discuss Insulation Resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

To the OP. If your part p registered how did you pass the assessment? Testing is one of the main requirements and especially understanding the results. If you did pass it and are a domestic installer this still doesn't make you a qualified electrician. I should of put the last bit in pet hates.
 
When Mars is closest to the Earth, it takes light three minutes to travel between the two planets. If you asked a question to an astronaut on Mars, you'd have to wait at least six minutes for an answer, and Mars is usually a lot farther away than that.
 
in the sequence of tests before the supply ois connected it doesnt state rcd testing comes first
i continutiy oc protective conductors
2continuity of ring
3ir
4pol
5 earth electrode
 
in the sequence of tests before the supply ois connected it doesnt state rcd testing comes first
i continutiy oc protective conductors
2continuity of ring
3ir
4pol
5 earth electrode

who said it came first andy? the fact you gave a 0.2 reading was why we asked what the real readings were, now we know what 0.2 has to do with a TT system, but 1 do you? and 2 what has your IR readings mean to you?
 
If your insulation tests are poor it is little wonder you aint done any RCD testing. Anyway you originally said you had done RCD testing and you got 0.2 whatever you claim that is supposed to signify!
 
one of the posters in this topic stated i shouldnt be doing anything if i havent done rcd tests

No we asked you to confirm your RCD readings before we would give you any help andy as the reading you gave was at best confusing and you got the 0.2 mixed up from something else to do with them??
 

Reply to Insulation Resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
619
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
834
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
753
I’ve had a weird one today. Banjo having 50v on it. L - main earth = 230v L - N = 230v N - main earth = clear I have 50v on the live - banjo &...
Replies
4
Views
631
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock